Is this multi wired circuit wired correctly?


  #1  
Old 01-31-11, 01:55 PM
C
Member
Thread Starter
Join Date: Jan 2011
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is this multi wired circuit wired correctly?

I'm running a multi wire circuit to my shed. I have 4 wires (black, red, green, and white). I will have both hots going into a 20 amp dpst switch. After the first GFCI, I am going to run 2 or 3 more outlets for power tools. After the second, I am going to run some lights. I just want to know if I am doing this correctly. Is the diagram acceptable?


multiwirecircuit.png picture by cec78 - Photobucket
 
  #2  
Old 01-31-11, 02:10 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Your diagram looks correct to me.
 
  #3  
Old 02-01-11, 01:22 PM
W
Member
Join Date: Jun 2008
Location: VA.
Posts: 765
Upvotes: 0
Received 1 Upvote on 1 Post
Your diagram looks correct as far as the receptacles are concerned but, I don't see how you intend to feed the lights. In your post it appears as you're going to protect the lights with the GFI however, only the receptacles need to be protected not the lights.

You want to feed the lights from the line side of one of your GFI's so if it trips you won't be in the dark.

PS. Don't forget to use a double pole breaker in your house panel.
 
 