Question GFCI breaker reversed?

Hi,

I have had a strange problem and greatly appreciate any helps here.
There are 4 receptacles in my bathroom, one with a GFCI breaker in it. I plugged in a 1500W heater last night and it lost power after ~20 minutes. I tried to reset the GFCI breaker but the power still didn't come to those receptacles. This morning, I noticed that when I pushed the "test" button on the GFCI breaker, the receptacle with the GFCI powered up, but not the other three. When I push the "reset" button, all 4 receptacles lost power. Does this mean that the GFCI is broken or something else is wrong?

Thanks.
 
  #2  
Old 02-10-11, 03:49 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
I suspect the large load placed by the heater on a connection in the circuit caused it to fail. I would turn off the breaker and start looking for a loose connection. This could be at the last working or first non-working receptacle.
 
  #3  
Old 02-10-11, 03:51 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
Did I read it correctly? You have both a GFCI breaker AND a GFCI receptacle?
 
 