Romex 14-2 G in a garage with a 20 amp breaker

I have to add some floodlights to our detached garage. The whole garage is on a 20 amp breaker. However, I see a lot of 14-2 G and some 14-3 G cabling in the garage. The garage is unfinished so all the cabling is exposed. Is it not inconsistent to have the 14 gauge wiring with a 20 amp breaker? Can this cause trouble?
 
  #2  
Old 03-05-11, 02:16 PM
B
Member
Join Date: Feb 2011
Location: USA
Posts: 50
Upvotes: 0
Received 0 Upvotes on 0 Posts
14 gauge wire should NOT be on a 20 amp breaker for a general purpose circuit. Under heavy loads the wire will overheat before the breaker trips. Change the breaker to a 15 amp or upgrade all the wiring to 12 gauge.
 

Last edited by pcboss; 03-05-11 at 03:24 PM. Reason: technical correction
  #3  
Old 03-05-11, 04:22 PM
R
Member
Thread Starter
Join Date: Nov 2002
Location: USA
Posts: 118
Upvotes: 0
Received 0 Upvotes on 0 Posts
If the original electricians (1994) had consistently used 12 gauge to the wall outlets and only used 14 gauge to the lights in the garage and the outside spotlights, would we then be okay? I see some 12 gauge to the GFCI and other outlets (these are Essex cables) and not all have readable markings, but I do not know what they used to the garage door openers. We have not had problems in the garage in the four years we have been here, but we do not have heavy equipment such as a wood shop in the garage.
 
  #4  
Old 03-05-11, 06:16 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,414
Received 163 Upvotes on 142 Posts
The important thing is that the breaker is properly sized to the wire. A wire with a breaker that is too high of an ampacity could overheat and potentially cause a fire before the breaker tripped.
 
  #5  
Old 03-05-11, 09:03 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 37 Upvotes on 29 Posts
The first thing to do is to absolutely ascertain which circuit breaker controls power to the various cables. You may be mistaken in thinking that the #14 is on a 20 ampere breaker.
 
  #6  
Old 03-06-11, 02:01 PM
R
Member
Thread Starter
Join Date: Nov 2002
Location: USA
Posts: 118
Upvotes: 0
Received 0 Upvotes on 0 Posts
I greatly appreciate the timeliness and cogency of the replies I received. Sure enough I did more homework and found that the garage does have both a 15 amp and a 20 amp breaker. So I presume that all 12 gauge is to the plug-in boxes, and all the 14 gauge is to the lights. A spot check to one of the boxes showed this to be true. All the cables are white, so I have to look at the markings on the cable to see the gauge. Thank you.
 
 