Special GFCI for Sump Pumps?

Reply

  #1  
Old 03-13-11, 01:35 PM
ray2047's Avatar
Group Moderator
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 32,659
Special GFCI for Sump Pumps?

In post #9 in thread http://forum.doityourself.com/wells-...lled-gfci.html it was written by
Waterwelldude
About five years ago we had this issue come up at a water system in the city. The pump had to be on a gfci.
The pump would not run when placed on the gfi.
We replaced the pump witch was only 6 months old with a new one. Within a week the same thing happened.
We have now learned the there is a gfi that is made for this type of environment. The of the shelf gfi, will not work with submersible pumps. 99% of subs have some leakage and will trip a gfi.
A (good) electrical supply store should know witch gfi will work on the water pump.
Is this a unit with a higher trip threshold? Is it a commercial only exception similar to the no GFCI required one for sump pumps in elevator pits?
 
Sponsored Links
  #2  
Old 03-13-11, 02:32 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
The GFI being referred to may be a 30 mA trip GFI breaker, but as far as I know, they are only allowed on fixed heat trace and ice/snow melting equipment. These are for equipment and not personnel protection. Personnel protection requires a 6 mA trip GFI.
 
  #3  
Old 03-13-11, 06:29 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,359
Like CJ I think they might have used Class B 30 mA instead of the Class A 5mA that is needed for life safety.
 