Breaker size for 15 amp single phase

I have a new air compressor with a 3.5 HP single phase motor that says 15 amps on the motor sticker. I ran 10-3 wire from my panel to a disconnect box and the wire run was 55 feet. I installed a 20 amp double pole breaker in the panel. Will that be a big enough breaker to keep it from tripping on start up?
 
Sponsored Links
  #2  
Old 03-14-11, 07:54 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,669
It should be large enough. No need for 3 conductor cable on a 240 line.
 
  #3  
Old 03-14-11, 07:59 PM
Member
Thread Starter
Join Date: Mar 2011
Location: USA
Posts: 3
Thanks for the reply. I didn't know for sure on the wire so I figured it was better to have a little bigger and 3 conductor wire. Electrical confuses me but I'm learning.
 
  #4  
Old 03-18-11, 04:51 PM
Member
Thread Starter
Join Date: Mar 2011
Location: USA
Posts: 3
Got it hooked up and works great!
 
  #5  
Old 03-18-11, 06:02 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,669
Originally Posted by dhanna6 View Post
Got it hooked up and works great!
Good job. Thanks for letting us know.
 