how many outlets above a 7 foot countertop - 1 or 2

Reply

  #1  
Old 04-02-11, 07:57 AM
Member
Thread Starter
Join Date: May 2010
Location: United States
Posts: 37
how many outlets above a 7 foot countertop - 1 or 2

I am adding on a countertop to a 7' wall. I am confused as to whether I can legally have one outlet only, or if I need two. If I stick the outlet in the dead center of the wall, then that means there is 3.5' to the left and right of it...does that then meet the 4' requirement? I also thought that any appliance on the counter needs to be able to reach an outlet within 2' of its location, so then one outlet would not meet that requirement. Did I misunderstand the NEC code? Any professional advice on whether I need one or two would be appreciated,
thanks alot
 
Sponsored Links
  #2  
Old 04-02-11, 08:08 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
Is there a sink on this countertop?
 
  #3  
Old 04-02-11, 08:49 AM
Member
Thread Starter
Join Date: May 2010
Location: United States
Posts: 37
No, it is just a straight shot of countertop.
 
  #4  
Old 04-02-11, 10:20 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
You need a receptacle within 24" of both ends and no more than 48" in between each receptacle.
 
  #5  
Old 04-02-11, 03:38 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,279
Code requires counter space along a wall not be further than 24" from a receptacle. (Measured along the wall) You therefore need at least 2.
 
  #6  
Old 04-02-11, 03:44 PM
Member
Thread Starter
Join Date: May 2010
Location: United States
Posts: 37
Thanks all, that's what I thought. I found a closed junction box on this wall, but unfortunately when I checked to see what breaker it was on and what else was on the line, I found that it was on the line that controlled lighting above the sink, plus it was only 15a, and I think countertop receptacles need 20a and can't share the line with lighting fixtures. Looks like I am going to need a separate line. (unfortunately I should have asked this question *before* I put up the two 18" x 66" wall cabinets, ugh. Running wire now will be a pain.
 
  #7  
Old 04-02-11, 08:43 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
You are correct on both counts. The countertop circuit must be 20 amps and connot share lighting loads.
 
  #8  
Old 04-04-11, 09:49 AM
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 18,758
More recepacles is almost always better - in this case, code says you need two anyway but I would have said go with two even if code didn't require it, I always over-wire and have never regretted having the extra receptacles
 