GFCI Replacement Problem

I have a GFCI outlet in my master bathroom that had issues and recently replaced. On the load side there is 1 light switch and 2 standard receptacles. Before I replaced the GFCI it would not reset and I checked all the connections in each receptacle but couldn't find any problems. Now, after replacing the GFCI all the receptacles and switch get power but when the GFCI is tripped the receptacles and switch on the load side are still hot. Only the GFCI itself is dead. The GFCI receptacle has 2 black, 2 white and a ground wire. There was also one difference I noted between the old and new GFCI outlets. The old one only had 1 hole in for each screw to insert a wire and tighten it for a total of 4 places to insert wires. The new one has 2 per screw for a total of 8 places to put wires. Do I just have the GFCI miswired or would there be another problem I need to look into for the load components not going dead when the GFCI trips? Thanks
 
Sponsored Links
  #2  
Old 04-10-11, 07:30 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,590
It sounds like the wires going to the downstream receptacles are wired into the LINE terminals instead of the LOAD side. Load terminals provide the protection to items downstream.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes