I have an electrical box in the basement but its mounted flush with the stud. Should the box be move so its flush with the drywall or can a bigger hole be cut in the drywall and longer screws used to attach the outlet to the electrical box?
 
  #2  
Old 04-10-11, 07:33 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,332
Received 877 Upvotes on 740 Posts
If you can easily move the box so it will be flush with the drywall, I would do it. Otherwise, you can use a box extender and longer screws to mount the device. Code requires boxes to be no more than 1/8" set back from the face of the drywall and the box extender satisfies this requirement.
 
  #3  
Old 04-10-11, 07:33 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Mudring.. See Tolyn's answer. We posted at the same time. His gives more detail.
 
  #4  
Old 04-11-11, 04:24 AM
G
Member
Thread Starter
Join Date: Apr 2011
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks alot. This worked great.
 
 