Re-Wiring an old kitchen - question about furred-out walls
We are currently remodeling our kitchen, and have reached the point of electrical rough-in.
In order to maintain required clearance for an island, fridge, etc, the masonry walls have been furred out with 2x2's instead of re-framing with 2x4's. Yes, the cumulative 4 inches made a huge difference in layout.
Walls in question are 3 courses of brick, 2x2 PT furring strips, with soon-to-be 1/2" drywall on top.
Now, however, comes the question of how to wire this while maintaining code compliance.
I've got the wiring laid out such that I am able to utilize nothing but 1 1/2" deep metal boxes with 1/2" plaster rings and not go over on box fill (whew).
From what I understand, stapling NM cable directly to masonry is not a great idea, although by doing this, from what I can tell, would give the required 1 1/4" setback.
Would using AC (BX, what have you) alleviate the 1 1/4" setback issue?
Any thoughts, besides framing out with 2x4" and going that route (already had that argument with the wife, and I lost.)
Thanks for any help!!!
In order to maintain required clearance for an island, fridge, etc, the masonry walls have been furred out with 2x2's instead of re-framing with 2x4's. Yes, the cumulative 4 inches made a huge difference in layout.
Walls in question are 3 courses of brick, 2x2 PT furring strips, with soon-to-be 1/2" drywall on top.
Now, however, comes the question of how to wire this while maintaining code compliance.
I've got the wiring laid out such that I am able to utilize nothing but 1 1/2" deep metal boxes with 1/2" plaster rings and not go over on box fill (whew).

From what I understand, stapling NM cable directly to masonry is not a great idea, although by doing this, from what I can tell, would give the required 1 1/4" setback.
Would using AC (BX, what have you) alleviate the 1 1/4" setback issue?
Any thoughts, besides framing out with 2x4" and going that route (already had that argument with the wife, and I lost.)
Thanks for any help!!!
#2
Any thoughts, besides framing out with 2x4" and going that route (already had that argument with the wife, and I lost.)
#3
Member
Thread Starter
Join Date: May 2011
Location: USA
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Okay - am I reading something incorrectly, or do you think I could simply use plastic standoffs on the sides of the 2x2's to hold the cable in the cavity?
I guess I could bend EMT, but going around windows to get to the sink area is going to be a new 'art' for me to learn...
I guess I could bend EMT, but going around windows to get to the sink area is going to be a new 'art' for me to learn...

#4
I guess I could bend EMT, but going around windows to get to the sink area is going to be a new 'art' for me to learn...

#6
Member
Thread Starter
Join Date: May 2011
Location: USA
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Okay - last post of questions on this subject (I think):
One length of romex per conduit, otherwise it could be considered bundling?
Terminating the EMT at the ceiling, using a bushing of course, would be fine - no need to run it into an (accessible) box to break out of the tubing?
And last, but not least, secure the EMT to the brick with straps every 4.5'?
One length of romex per conduit, otherwise it could be considered bundling?
Terminating the EMT at the ceiling, using a bushing of course, would be fine - no need to run it into an (accessible) box to break out of the tubing?
And last, but not least, secure the EMT to the brick with straps every 4.5'?
#7
One length of romex per conduit, otherwise it could be considered bundling?
#8
Terminating the EMT at the ceiling, using a bushing of course, would be fine - no need to run it into an (accessible) box to break out of the tubing?
And last, but not least, secure the EMT to the brick with straps every 4.5'?
#9
You also use thhn in conduit because it is cheaper AND individual conductors carry more amps per nec than RX.
17c/ft for indivual conductors while ~$100 for 250' RX
17c/ft for indivual conductors while ~$100 for 250' RX
#12
Member
Thread Starter
Join Date: May 2011
Location: USA
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hmm - following the graphic from Mike Holt, and after hearing from my inspector that this is a 'grey' area and that they pass work done as shown by Holt:
Is aluminum clad MC (aka MC-Lite) acceptable for contact with Masonry? I do not see an individual designation in the IRC or NEC about it, and can't find much info on Southwire's website either.
I don't feel comfortable running NM along brickwork - afraid over time the NM will abrade and fail.
Is aluminum clad MC (aka MC-Lite) acceptable for contact with Masonry? I do not see an individual designation in the IRC or NEC about it, and can't find much info on Southwire's website either.
I don't feel comfortable running NM along brickwork - afraid over time the NM will abrade and fail.
#13
MC should is okay for surface mount on the masonry. I personally think that plan would be just fine and if the inspector is okay with it, then go for it. He is right that the code is not explicit in this situation, using vague terms like "subject to damage". The intent is to let the inspector decide on the individual case.
#14
In my area the AHJ has made it clear that aluminum armored MC cables are not suitable for use on masonry or concrete surfaces so in those applications MC Tuff (steel sheathed MC cable) is commonly used. The decision is based on
http://www.acewireco.com/pdfs/AFCCATALOG.pdf
PVC jacketed MC cable would also work, but the price is somewhat higher.
That being said, I frequently see installations of aluminum MC cables on masonry and concrete that has passed inspection. When you have many inspectors, some points and issues can get overlooked and some inspectors nitpick the fine points more than others.
Type MC Cables – Uses Not Permitted:
• Where exposed to destructive corrosive
conditions unless the metallic sheath is
suitable for the conditions or is protected
by material suitable for the conditions (page 3)
• Where exposed to destructive corrosive
conditions unless the metallic sheath is
suitable for the conditions or is protected
by material suitable for the conditions (page 3)
PVC jacketed MC cable would also work, but the price is somewhat higher.
That being said, I frequently see installations of aluminum MC cables on masonry and concrete that has passed inspection. When you have many inspectors, some points and issues can get overlooked and some inspectors nitpick the fine points more than others.
#15
Member
Thread Starter
Join Date: May 2011
Location: USA
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wel, kitchen is complete, and electrical passed first round, no questions asked.
Thanks for all the advice on the forums.
I spoke with the inspector here and found that the 1 1/4" IRC rule can be satisfied with the halex standoffs. Using these proved better than any other option. So, a few nail guards, a bunch of plastic standoffs, and about 300 ft of romex later, all is well.
Thanks again for all the advice.
I spoke with the inspector here and found that the 1 1/4" IRC rule can be satisfied with the halex standoffs. Using these proved better than any other option. So, a few nail guards, a bunch of plastic standoffs, and about 300 ft of romex later, all is well.
Thanks again for all the advice.