Cool generator panel question???

i have all the correct equipment i just have a question about if it is ok to tie all of your neutrals and grounds together or if you are supposed to have seperate neutral and ground bars (if so i would have to add one..) or do i just tie them all together on the one bar that came in the generator panel. i just dont know if there would be a neutral backfeed into the main panel or if that makes any difference? thank you..
 
Sponsored Links
  #2  
Old 05-11-11, 07:09 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Grounds and neutrals only get tied in the main panel. They need to be seperate after the main, and the neutral must be insulated from the panel.
 