Question 50 amp rv service

I'm trying to install 50 amp service in my workshop to provide power to my RV. I currently have a 50 amp double pole breaker installed in the panel to provide power for a welder I never bought. The receptacle has 2 110 legs (black and red) and a white neutral. Only problem is there is no bond wire. How would I go about providing a proper bond for the service? Also, the cord from the RV says there are three # 6 conductors (black, red, white) and one #8 conductor, I assume for the bond.

Thanks,
 

Last edited by fishman22; 05-25-11 at 02:39 PM. Reason: correct information
Sponsored Links
  #2  
Old 05-25-11, 02:47 PM
Member
Thread Starter
Join Date: May 2011
Location: USA
Posts: 4
I misspoke in my original post. I know that normally with a 220v line, there is no neutral. There are 2 110v legs and a bond. I used the black and red as the 110v hot leads and the white as the bond. That's how the welder receptacle was wired. Now I need to take the white bond, remove it from the bond buss bar and relocate it to the neutral bar, providing the required neutral for proper wiring service to the RV. Again, that leaves me without a bond for the RV. The receptacle for the RV is a 14-50R - 2 110v hot legs across from each other, the neutral on the bottom and the bond (half round) at the top.

Again thanks, and I'm sorry for the misinformation in the first post.
 
  #3  
Old 05-25-11, 02:58 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,295
If the wiring method is all metal conduit and boxes, that will suffice as the equipment ground (bond as you called it). All you would need to do in that case is run a #10 copper jumper from the ground terminal on the 14-50 receptacle to the ground screw in the metal junction box.

If you have a partial or complete plastic wiring method (romex cable, etc), you'll need to run a retrofit ground wire from the 14-50 receptacle back to the ground bus in the garage panel. This wire should be a green insulated #10 copper wire. It should be run in such a way to protect from damage, supported by staples. If you have access to the existing cable, I would tie-wrap the new ground right to the existing cable.
 
  #4  
Old 05-25-11, 03:00 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
You'll need to run a new 4 wire cable from the box to the old welder receptacle, and provide a 4 prong receptacle so the plug you have will mate up to it.
Ben beat me to it. I wasn't thinking of conduit, just cabling.
 
  #5  
Old 05-25-11, 05:55 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,653
2 110v hot legs across from each other,
Just for clarity those are not the 110v hot legs. They are the 240v hot legs. The 120v comes from either of the 240v legs and the neutral.
 
  #6  
Old 05-25-11, 06:26 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
If you have a partial or complete plastic wiring method (romex cable, etc), you'll need to run a retrofit ground wire from the 14-50 receptacle back to the ground bus in the garage panel. This wire should be a green insulated #10 copper wire. It should be run in such a way to protect from damage, supported by staples. If you have access to the existing cable, I would tie-wrap the new ground right to the existing cable.
I do not like this method as someone might say what's this wire for and just snip it. I would just replace the cable, especially if it is a short run.
 
  #7  
Old 05-26-11, 09:22 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,295
Who walks around their house snipping random wires? If so, they deserve what they get.

A retrofit ground is allowed by NEC art. 250.130(C).
 