Older Stove Wiring Question

I just purchased a house built in 1996 so it has the 3 prong for the range. The range is wired with one white, one black, and a ground. I found this odd as I thought it should be one red, one black, and a white (for neutral). So there is no neutral only a ground and the stove is connected with the white (as hot), black (as hot), and the ground bare wire where the neutral would go.
Is this a problem? The stove seems to function properly but I wanted to see if I needed to get this changed.
Thanks!
 
Sponsored Links
  #2  
Old 05-27-11, 09:52 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Your situation was never allowed by the code, however many jurisdictions did approve the installation with the bare neutral. You are correct that it should have been black, red, white. You can replace it if you want, but as long as it was approved by the original inspector at construction it will remain grandfathered until you remodel the kitchen. There are a lot of houses with the range installed just like yours.
 
  #3  
Old 05-27-11, 12:21 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,943
Received 30 Votes on 26 Posts
Is the ground a bare copper or a stranded aluminum conductor? I would have thought given the age of your house the wiring would have been up to the current 4 wire requirements which IIRC pre-date your house.
 
  #4  
Old 05-27-11, 04:36 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
My range is wired just like that with no problems. I would still like it to be 4-wire, however.
 
  #5  
Old 05-27-11, 06:26 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,042
Received 26 Votes on 20 Posts
I have seen a few drywers wired like that too, with 10-2/G romex. Just because it works doesn't mean it's right.
 
  #6  
Old 05-27-11, 06:51 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,965
Received 59 Votes on 52 Posts
Originally Posted by CasualJoe View Post
Just because it works doesn't mean it's right.
But is was right when it was originally installed. The OP's location may have been on an older code than 1996.
 
  #7  
Old 05-27-11, 07:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,943
Received 30 Votes on 26 Posts
I think it needs to be known if this is NM or SE. One was allowed, but not the other.
 
  #8  
Old 05-28-11, 08:19 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,042
Received 26 Votes on 20 Posts
Originally Posted by Tolyn Ironhand View Post
But is was right when it was originally installed. The OP's location may have been on an older code than 1996.
That was more of a generic statement, but considering there was one black, one white and one ground, it sounds like NM cable which was never right by NEC as far as I know, regardless of passing a local inspection.

The range is wired with one white, one black, and a ground.
If what was stated to be a ground was an insulated neutral, then yes, it could have been right at that time, but it doesn't sound like that is the case..
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: