Outdoor Temporary Service To Camper

Reply

  #1  
Old 06-02-11, 04:24 PM
63zerb's Avatar
Member
Thread Starter
Join Date: Mar 2008
Location: Eastern PA.
Posts: 39
Outdoor Temporary Service To Camper

My In Laws are coming from AZ to stay with us in PA. They will be in a camper in our yard for two months. The total run from panel box to camper is about 115 feet. I am not sure but I think the plug on camper is 30 amp (see pics) Is the correct wire size 10-2 for 30 amp? Should this be protected by GFCI breaker? Can some one explain label on camper (see pic) It says about the connection for 110 125 volt A/C Do not connect to higher voltage. (Hope pics work not sure if URL business is correct.)
 
Sponsored Links
  #2  
Old 06-02-11, 04:38 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
Use this to post pix on your post> http://www.doityourself.com/forum/el...your-post.html
 
  #3  
Old 06-02-11, 05:37 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
Are you planning on installing a small RV receptacle on a post or using a cord?
 
  #4  
Old 06-02-11, 07:02 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,678
Hope pics work not sure if URL business is correct.
It wasn't. Must be in jpg, gif or png format for embedding.

 
  #5  
Old 06-04-11, 04:30 AM
63zerb's Avatar
Member
Thread Starter
Join Date: Mar 2008
Location: Eastern PA.
Posts: 39
Plug would be installed on a post concreted in with embedded 3/4 conduit to two gang outdoor box.
 
  #6  
Old 06-04-11, 04:43 AM
63zerb's Avatar
Member
Thread Starter
Join Date: Mar 2008
Location: Eastern PA.
Posts: 39
pics


can anyone open these?



 

Last edited by GregH; 06-04-11 at 06:34 AM. Reason: Edit url for pics to show in post
  #7  
Old 06-04-11, 05:06 AM
Member
Join Date: Feb 2006
Location: USA
Posts: 6,282
Pics

Nope. Use Chandler's instructions posted above.
 
  #8  
Old 06-04-11, 05:20 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,991
Originally Posted by 63zerb View Post
Plug would be installed on a post concreted in with embedded 3/4 conduit to two gang outdoor box.
If you run PVC conduit, you will have to bury it 18" down and run 3 #10 THHN/THWN wires (Hot/Neutral/Ground). The conduit run will have to be continuous to run the THHN. Most cases it is helpful to run Romex from the panel to a box on the outside of the house and then convert it to the individual conductors. I also suggest using stranded wire.

OR you could run 10/2 w/G UF cable the entire way. That will be required to be buried 24" The cable will be required to be protected on each end with conduit.
 
  #9  
Old 06-04-11, 05:26 AM
Member
Join Date: Feb 2006
Location: USA
Posts: 6,282
30 Amp RV Receptacle

Here is a good write-up on the subject:

RV Electric

Click on the 30 amp link on the left.

Hope this helps.
 
  #10  
Old 06-04-11, 07:11 AM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
You could use an 100' 30A extension cord if it is only temporary.(90 days or less) IIRC, travel trailers already have a 20'cord. Just install a tt-30 somewhere on your house. You will need to portect your cord connections, too.
 