My In Laws are coming from AZ to stay with us in PA. They will be in a camper in our yard for two months. The total run from panel box to camper is about 115 feet. I am not sure but I think the plug on camper is 30 amp (see pics) Is the correct wire size 10-2 for 30 amp? Should this be protected by GFCI breaker? Can some one explain label on camper (see pic) It says about the connection for 110 125 volt A/C Do not connect to higher voltage. (Hope pics work not sure if URL business is correct.)
#8
OR you could run 10/2 w/G UF cable the entire way. That will be required to be buried 24" The cable will be required to be protected on each end with conduit.
#9
Member
30 Amp RV Receptacle
Here is a good write-up on the subject:
RV Electric
Click on the 30 amp link on the left.
Hope this helps.
RV Electric
Click on the 30 amp link on the left.
Hope this helps.
#10
You could use an 100' 30A extension cord if it is only temporary.(90 days or less) IIRC, travel trailers already have a 20'cord. Just install a tt-30 somewhere on your house. You will need to portect your cord connections, too.