Two different circuits in a receptacle 2 gang box?

Is it against code to have 2 receptacles in the same two gang box, each on a different circuit?

I am about to install a thru-wall air conditioner. I am running a home run for the AC unit. The side of the unit that has the power cord will end up right over an existing duplex receptacle. It thought is would look odd to have two, one-gang receptacles right next to each other, so I was thinking of converting the existing one gang to a two gang. But, each receptacle will be on a different circuit. Is that OK?

Also, I was thinking of using a single outlet receptacle for the AC circuit, to help tell the AC circuit from the existing circuit. Would it be against code to have a home run to a single receptacle circuit?

Thanks,
Guy
 
Sponsored Links
  #2  
Old 06-11-11, 12:56 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,972
Received 59 Votes on 52 Posts
You may have 2 receptacles, in the same box, fed with two circuits.

In fact you can even have one duplex receptacle fed with two circuits. You are required to handle tie (IE: use a two pole breaker) so that all the hots feeding that device will be disconnected at the same time.

A single receptacle may be fed with a dedicated circuit. If it is a 20 amp circuit, you would be required to use a 20 amp single receptacle.
 
  #3  
Old 06-11-11, 01:00 PM
Member
Thread Starter
Join Date: Nov 2004
Location: Pleasantville, NY
Posts: 548
Received 0 Votes on 0 Posts
Thanks.

The unit is a 10,000 BTU unit, with a parallel plug. I was going to use a 15 amp receptacle with 14/2 wire. Do you think that will be OK?
 
  #4  
Old 06-11-11, 01:20 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,955
Received 33 Votes on 28 Posts
What is the nameplate data? Is the cord end a 15 or 20 amp?
 
  #5  
Old 06-11-11, 01:51 PM
Member
Thread Starter
Join Date: Nov 2004
Location: Pleasantville, NY
Posts: 548
Received 0 Votes on 0 Posts
The data says 115V, 8.2 amp. The plug looks like a 15 amp plug, where both blades are the same size.
 
  #6  
Old 06-11-11, 02:23 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
Number 14 wire with a 15 ampere circuit breaker and receptacle is acceptable. I would probably use number 12 with a 20 ampere circuit breaker and receptacle to be certain of compensating for voltage drop but it is not absolutely necessary. I've run a 10,000 BTU window unit on a 15 ampere general purpose circuit with no problem.
 
  #7  
Old 06-11-11, 02:33 PM
Member
Thread Starter
Join Date: Nov 2004
Location: Pleasantville, NY
Posts: 548
Received 0 Votes on 0 Posts
Thanks a million for all replies.
 
  #8  
Old 06-11-11, 08:27 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
At my old house, everytime the 14,000btu a/c kicked on, I would end up running down to the basement to reset the 15A breaker. Now, we have no problem with the a/c on a 20A breaker.
 
  #9  
Old 06-11-11, 09:35 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
14,000 is 40% more than 10,000.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: