Moving Cold Water Pipe Ground Wire

I need to remove the cold water pipe that my breaker panel is grounded to. After I remove the pipe, I am going to ground the panel to the next nearest cold water pipe.

Do I need to take any precautions during the time the old connection is removed and the new connection completed (should take about 15 minutes)?
 
Sponsored Links
  #2  
Old 06-19-11, 03:49 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
You night want to add a second ground using an eight foot ground rod first. In some places just a water pipe is no longer code so you will be bringing it up to code.
 
  #3  
Old 06-19-11, 05:00 PM
Member
Thread Starter
Join Date: Dec 2006
Location: Ohio
Posts: 232
Received 0 Votes on 0 Posts
It is grounded with an 8' ground rod and it is to code.

My question was should I take any precautions during the time the old connection is removed and the new connection completed (should take about 15 minutes)?
 
  #4  
Old 06-19-11, 05:32 PM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 21,119
Received 2 Votes on 2 Posts
If it's grounded through a rod as well...shouldn't be anything to be concerned about for a 15min timeframe. The Pro's will weigh in on whether you should have or even need both.
 
  #5  
Old 06-19-11, 06:17 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,059
Received 26 Votes on 20 Posts
Originally Posted by ruauu2 View Post
It is grounded with an 8' ground rod and it is to code.

My question was should I take any precautions during the time the old connection is removed and the new connection completed (should take about 15 minutes)?
If it's to code, I would assume the water pipe ground termination is where the water enters the house and is bonded with continuous ground wire across any pressure reducing valves and/or water meters. To answer your specific question, you shouldn't have a problem.
 
  #6  
Old 06-19-11, 08:19 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,948
Received 32 Votes on 27 Posts
I am going to ground the panel to the next nearest cold water pipe.
You need to make the connection within 5' of where the pipe enters the house, not the nearest pipe.

The conductor also needs to be continuous.
 
  #7  
Old 06-19-11, 08:24 PM
Member
Join Date: Oct 2005
Location: Milwaukee WI
Posts: 1,338
Received 0 Votes on 0 Posts
If you want belt and suspenders,
1. Turn off your main breaker.
2. Add a jumper (i.e. auto jumper cable) as a stand-in for the pipe you are removing.

Plumbers have good stories about removing water heaters and replacing water pipes in homes that have bad utility neutrals.

There is a remote chance that a nearby service with a bad neutral may also be finding ground through your water pipe as well.
 
  #8  
Old 06-19-11, 09:20 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
Originally Posted by pcboss View Post
You need to make the connection within 5' of where the pipe enters the house, not the nearest pipe.

The conductor also needs to be continuous.
PC., I thought it have to be 20 feet of contuinus copper pipe to treat as grounding electrode source.

Merci,
Marc
 
  #9  
Old 06-20-11, 12:27 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
The grounding electrode conductor must be attached to the incoming cold water pipe no more than five feet from where the pipe enters the building. The piping must have a minimum of ten feet (it could be twenty feet, it has been a long time since I checked) buried in order to use as a grounding electrode. Obviously the pipe needs to be metal, either copper or steel.
 
  #10  
Old 06-20-11, 09:49 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The 20' requirement is the minimum length of rebar embedded in the footing for a legal Ufer ground. The 10' requirement is how far the metal water pipe must extend into the ground horizontally to count as a legal ground. The 5' requirement is how close the grounding electrode conductor (ground wire) must connect to the water pipe when it enters the building.

It wouldn't hurt to clip a set of jumper cables from the water service pipe to the ground wire while you do the plumbing work you need to do.
 
  #11  
Old 06-20-11, 10:51 PM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes on 0 Posts
Thanks for correcting that one due I am used with French Codés.

Merci,
Marc
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: