I am having a well drilled and the well company notified me that they will leave me enough electrical wire from the pump to get me into my house. They are using a Franklin Electric J-Class 230V 1.5hp 20gpm pump. I contacted Franklin Electric and they told me I need a 30amp double breaker. The contractor told me they use 12/2 wire. Should they be using 12/2 or 10/2 wire? The well is being drilled to about 260feet. The well will be located approximately 50-75 feet from my panel. Thanks
Old 06-29-11, 08:07 AM
ray2047's Avatar
In this case it isn't the breaker size but the full load amps the pump draws after starting that determines wire size. If the FLA is under 20a you are probably OK. The breaker is probably sized to the starting or locked rotor amps.
Old 06-29-11, 09:06 AM
Either is okay in this case. If you have the option to upsize, I would, but it is not necessary that you do so.
Old 06-29-11, 05:38 PM
CasualJoe's Avatar
I think I would upsize the wire too simply for voltage drop since the length is over 300 feet.
Old 07-02-11, 01:10 AM
Ya right on border line but most single phase well pump motours can handle some VD { Voltage drop } but not too much unless you have 208 volts included in the nameplate then you are fine but it may be little harder to start especally with very hard water.
I will upgrade as well if the situation arise.
There one thing about well drillers they should carry a chart for the conductor size and distance with motour size there were few case I have to fix their goof espcally with super long runs.
Merci,
Marc
Old 07-03-11, 08:48 PM
The well may be 260' deep, but the pump may not be that deep in the well. My well is about 150', but the pump is at 80'.
Old 07-04-11, 08:52 AM
CasualJoe's Avatar
That could still make the circuit about 150 feet long. I'd still upsize the wire.