Replacing NEMA 14-50R w/NEMA 10-30, then attach Welder Leads that have 6-50R/P

I am replacing a 240 volt Nema 14-50R (3 wire plus ground) female with a Nema 10-30 female (3 pole, 3 wire, non grounding) receptacle. I have welder leads that will have a Nema 10-30 male plug and a Nema 6-50R female receptacle. The welder has a Nema 6-50P Male plug. It looks like the Nema 6-50R/P has a ground, a positive, and a negative post. If that is correct, how do I go from the three wire plus ground (Nema 14-50R)to the Nema 10-30 then to the Nema 6-50P? Thanks.....
 
Sponsored Links
  #2  
Old 07-09-11, 11:31 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
It looks like the Nema 6-50R/P has a ground, a positive, and a negative post.
No, two hots and a ground. Explain why you are trying to replace a 50 amp plug with a 30 amp plug. If it is to use a welder rated 50 amps on a 30 amp dryer circuit it is a bad idea. Neither the breaker or wiring are rated for your welder.
 
  #3  
Old 07-09-11, 11:48 AM
Member
Thread Starter
Join Date: Jul 2011
Location: USA
Posts: 14
Received 0 Votes on 0 Posts
I already had the leads with a Nema 10-30 male plug. Thought that would work and would just work to that end. What you are saying is: (1) don't replace the Nema 14-50R (2) put a Nema 14-50P instead of the Nema 10-30 male plug. Everything else should then work? If that is correct....how do I wire the three multi strand 10 gauge leads to finally get to the two hots and a ground for the Nema 6-50? The breakers are 50 amp.... Thanks for the quick response.
 
  #4  
Old 07-09-11, 12:50 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
No. If you have a device (welder, etc). that has a 50 amp plug then check the name plate. If the name plate says it can draw more the 40 amps you need a 50 amp receptacle on a 50 amp breaker wired with #6*. A 30a dryer receptacle doesn't come even close to that. What I am say is you need to run a new circuit for the welder assuming the plug that is on it is correct.

*In some cases #8 hard wired but in a residential setting best to match wire size to breaker.
 
  #5  
Old 07-09-11, 01:21 PM
Member
Thread Starter
Join Date: Jul 2011
Location: USA
Posts: 14
Received 0 Votes on 0 Posts
The welder has the 6-50P plug. Name plate says it can draw 47.5 amps. The receptacle on the wall is a 14-50R (3 wires plus a ground wire) connected to 50 amp breakers. I will get a 14-50P plug on one end of the leads to plug into the wall (14-50R). On the other end of the lead, I will put a 6-50R female receptacle. The welder has a 6-50P plug already on it that I will plug into the female end of the lead. Is that correct? How do I go from three wires plus ground (14-50 R/P) to the two wires plus ground (6-50R/P). Do I just use two hot wires (side slots) and ground (top round) on the 14-50P, then wire the 6-50 R/P with those two hot and one ground wire?
 
  #6  
Old 07-09-11, 01:26 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
Why not just replace the welder plug with a 14-50? It'll be alot cheaper.
 
  #7  
Old 07-09-11, 01:44 PM
Member
Thread Starter
Join Date: Jul 2011
Location: USA
Posts: 14
Received 0 Votes on 0 Posts
Originally Posted by Justin Smith View Post
Why not just replace the welder plug with a 14-50? It'll be alot cheaper.
I want to be able to use the 50 ft leads so that I can weld outside of the garage. Plus...that would be way too easy......
 
  #8  
Old 07-09-11, 02:49 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
How do I go from three wires plus ground (14-50 R/P) to the two wires plus ground
No connection to the silver "W". silver screw. If you are using 3 conductor service cable (black, white, green) the white is used as one of the hots, either X or Y.

Just curios you referenced NEMA 10-30 in your first post. Is this a new plan?
 
  #9  
Old 07-09-11, 03:13 PM
Member
Thread Starter
Join Date: Jul 2011
Location: USA
Posts: 14
Received 0 Votes on 0 Posts
Different plan from the original post. It was the plan that I was trying to say in post #3, after your first post telling me about using the 30 amp when I should stick with the 50. Just didn't get it across the way I needed to. I think you have me all fixed up now. As you can tell, I'm not an electrician. Actually hate messing with it. I like working with stuff I can see before it bites me. Really do appreciate your help......
 
  #10  
Old 07-09-11, 04:06 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Glad you are on the right track. Yep, some times I read posts too fast, sorry about that. Just a check you are using at least #10 cable* and it is service cable (example SOW) not Romex, correct?

*Assumes a short duty cycle welder.


Source 2008 NEC
 

Last edited by ray2047; 07-09-11 at 05:01 PM.
  #11  
Old 07-09-11, 05:30 PM
Member
Thread Starter
Join Date: Jul 2011
Location: USA
Posts: 14
Received 0 Votes on 0 Posts
Yep....I think it is 10 or 8. The electrician knew what the intent was for the outlet when I had the garage built. I will use your table and make sure everything is OK. Again...thanks for your help. First time I've used the DoItYourself forum. Really do like it. Know I will be back.....
 
  #12  
Old 07-09-11, 06:20 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Actually I was writing about the cable for the extension cord. Good luck and come back if you have anymore questions.

The electrician knew what the intent was for the outlet when I had the garage built.
Actually I was writing about the cable for the extension cord.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: