Welder Receptacle

Reply

  #1  
Old 07-24-11, 09:00 AM
Member
Thread Starter
Join Date: Feb 2006
Location: Near Sacramento,CA
Posts: 20
Welder Receptacle

I just purchased another welder and it will run on 110 or 220. The 220 plug plugs into a NEMA 6-50R and requires a 35 amp (25 amp time delay) fuse or breaker. My old welder plugs into a NEMA 6-50R and requires 50 amp service. Any ideas on how to use the same receptacle and protect each device. My only idea is to put a fused disconnect at the outlet and change fuses per welder. Any other ideas?
Thanks,
Randy
 
Sponsored Links
  #2  
Old 07-24-11, 09:03 AM
Member
Join Date: Aug 2009
Location: USA
Posts: 4,941
You can plug the new welder into the same outlet with no problem. The 35 amp requirement is a minimum. You can use it on a circuit rated at 50 amps.
 
  #3  
Old 07-24-11, 08:30 PM
Member
Thread Starter
Join Date: Feb 2006
Location: Near Sacramento,CA
Posts: 20
The welder manual says not to size the branch circuit protection by the plug rating, so I'm thinking they are protecting the welder at 35 amps.
 
  #4  
Old 07-25-11, 06:58 AM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
The welder manual says not to size the branch circuit protection by the plug rating, so I'm thinking they are protecting the welder at 35 amps.
I think 50A is fine. Maybe you would want to reduce to a 40A breaker, but you would have a real hard time finding a 35A fuse.
 
  #5  
Old 07-25-11, 09:19 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,296
Welders have a wide range of compatible breakers and circuits. What are the specs on the new welder? Specifically input amps and duty cycle. What is the make/model?

Your old welder plug is a 6-50 with 50A breaker, but do you know what AWG the wiring in the wall is? In some cases it might be as small as #12 which may or may not be okay for this welder.
 
  #6  
Old 07-25-11, 05:55 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,221
Originally Posted by Justin Smith View Post
I think 50A is fine. Maybe you would want to reduce to a 40A breaker, but you would have a real hard time finding a 35A fuse.
Any good supply house stocks them. Even Home Depot stocks them.

Find a Cooper Bussmann FRN Series 35 Amp Brass Time-Delay Fuse Cartridges (2-Pack) - BP/FRN-R-35 at The Home Depot
 
  #7  
Old 07-25-11, 06:37 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Any good supply house stocks them. Even Home Depot stocks them.
I thought they jumped from 30 right to 40. My bad.
 