Wiring a 15amp circuit with 12/2 to outlets and 14/2 and 14/3 to lights.

Wiring a 15amp circuit with 12/2 to outlets and 14/2 and 14/3 to lights.

Reply

  #1  
Old 09-07-11, 04:37 PM
Member
Thread Starter
Join Date: Sep 2011
Location: USA
Posts: 71
Received 0 Votes on 0 Posts
Wiring a 15amp circuit with 12/2 to outlets and 14/2 and 14/3 to lights.

I'm putting together an electrical plan so I can apply for a building permit to remodel my house and have a question on wire sizes.

I was told that it would be ok, on a 15 amp circuit to run 12/2 to the receptacles and then run 14/2 and/or 14/3 to a switched light. Is there anything wrong with this?

This is what I was planning in the kitchen.
 
Sponsored Links
  #2  
Old 09-07-11, 04:58 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
In general code wise no. Confusion wise for the next person yes. Someone else later on may see the number 12 and not realizing there is #14 also increase the breaker size two 20 amps. Best practice don't intermix wire sizes.

Moot point perhaps since this is a kitchen. There must be two 20 amp dedicated circuits for the counter top receptacles. Nothing else can be on those circuits.
 

Last edited by ray2047; 09-08-11 at 07:20 AM. Reason: Remove incrorect statement.
  #3  
Old 09-07-11, 05:06 PM
Member
Thread Starter
Join Date: Sep 2011
Location: USA
Posts: 71
Received 0 Votes on 0 Posts
So I should either up the wire size to the lights to 12 and/or install a 20amp breaker. That would also mean I'd have to install 20amp receptacles as well correct? The 20amp breakers are the same price as the 20amp. 20amp receptacles cost a bit more than the 15.

Counter top receptacles are fed by 2 20amp circuits, with a GFCI receptacle for the first receptacle in the circuit.
 
  #4  
Old 09-07-11, 05:14 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
That would also mean I'd have to install 20amp receptacles as well correct?
No. As long as there are two places to plug you are OK. A single duplex receptacle meets that requirement.
 
  #5  
Old 09-07-11, 05:20 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
I would just use all #12 on a 20A breaker. I hate working with 14 in general, yet intermixing it with 12 is a real pita. You do not need to use 20A receptacles on a 20A circut. You should also not use cheap (50c) 15A receptacles. The backwired ones with the pressure plates are best.
 
  #6  
Old 09-07-11, 08:43 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,955
Received 33 Votes on 28 Posts
Like Ray said, you will need a minimum of two 20 amp circuits to serve the kitchen receptacles. Lighting cannot be part of this circuit. I would install a 15 amp circuit for the lighting.
 
  #7  
Old 09-08-11, 03:23 AM
Member
Thread Starter
Join Date: Sep 2011
Location: USA
Posts: 71
Received 0 Votes on 0 Posts
I have a total of 4 circuits in the kitchen
2 20amp GFCI protected circuits for the counter top outlets, and only the counter top outlets, nothing else will be on this circuit
1 20amp circuit dedicated for the refrigerator
1 15amp circuit for non-counter top outlets and 1 ceiling light


I'm going to increase the wire size to the lights to 12 so the entire circuit is the same wire size.
 
  #8  
Old 09-08-11, 06:01 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,955
Received 33 Votes on 28 Posts
Originally Posted by drummin89 View Post
I have a total of 4 circuits in the kitchen
2 20amp GFCI protected circuits for the counter top outlets, and only the counter top outlets, nothing else will be on this circuit
1 20amp circuit dedicated for the refrigerator
1 15amp circuit for non-counter top outlets and 1 ceiling light


I'm going to increase the wire size to the lights to 12 so the entire circuit is the same wire size.
Lighting and receptacle circuits cannot be mixed in the kitchens and dining rooms.
 
  #9  
Old 09-08-11, 07:48 AM
Member
Thread Starter
Join Date: Sep 2011
Location: USA
Posts: 71
Received 0 Votes on 0 Posts
Can the dining room and kitchen share a lighting circuit?
 
  #10  
Old 09-08-11, 09:28 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
Lighting can be shared throughout the house provided it is not also on a receptacle circuit that is required to be dedicated.

In other words, only specific receptacle circuits need to be dedicated and all other circuits (lights and receptacles) may be shared.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: