Question 60amp branch circuit

Can i use 3 12awg wire in place of 1 6awg wire in a 75ft run in conduit. It would be 4 strands of 3 12awg wire to take the place of 6/1 wire?
 
Sponsored Links
  #2  
Old 09-19-11, 04:00 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,646
No, you can not.

................
 
  #3  
Old 09-19-11, 04:43 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Only conductors 1/0 or larger can be paralelled.
 