GFCI that doesn't seem right

I have a GFCI in the kitchen where my refrigerator is plugged into it. There is another outlet on that same circuit.

Now this is where something isn't right.

When I test the GFCI by pushing the off button it turns off the other outlet but not itself where the frig is plugged into.

Thanks
 
  #2  
Old 09-21-11, 10:28 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Pull the receptacle and using a meter or test light determine which cable is hot. Are both the black and white of the hot cable connected to the line side?
 
  #3  
Old 09-21-11, 11:33 AM
T
Member
Thread Starter
Join Date: Mar 2007
Location: Louisville KY
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the quick reply Ray.

NO. The hot cables are connected to the load side.

Rock
 
  #4  
Old 09-21-11, 12:00 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
I've never seen this particular problem. I can only guess that contacts are welded in the GFCI mechanism and the receptacle must be replaced.

How did you come upon this problem? Were you just checking the GFCI test buttons or is it part of a different electrical problem you were troubleshooting? What kind of tester did you use to verify the GFCI receptacle still had power after the TEST button tripped?
 
  #5  
Old 09-21-11, 12:25 PM
T
Member
Thread Starter
Join Date: Mar 2007
Location: Louisville KY
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
I was just checking the GFCI to see if it was working properly. I have the refrigerator plugged into the GFCI and a lamp in the outlet downline. When I tripped the GFCI the lamp went out but the frig kept running and when I opened the door the light came on.

Thanks
Rock
 
  #6  
Old 09-21-11, 12:28 PM
belgarid's Avatar
Member
Join Date: Aug 2011
Location: USA
Posts: 115
Upvotes: 0
Received 0 Upvotes on 0 Posts
If the hot wires are on the load side, then it is wired wrong. The hot wires should be connected to the line side and anything that you want protected downstream of the GFCI should be connected to the load side.
 
  #7  
Old 09-21-11, 12:29 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
NO. The hot cables are connected to the load side.
Oh wait, you said the hot wires are on the LOAD side? That's backwards.

The hot and neutral wires with incoming power should be on the LINE side of the GFCI receptacle. The wires going to the downstream receptacle(s) should be on the LOAD side.
 
  #8  
Old 09-21-11, 01:39 PM
T
Member
Thread Starter
Join Date: Mar 2007
Location: Louisville KY
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is it possible the previous owner intentionally wired it backwards so if it was unknowingly tripped the food in the refrigerator wouldn't spoil?
 
  #9  
Old 09-21-11, 04:06 PM
belgarid's Avatar
Member
Join Date: Aug 2011
Location: USA
Posts: 115
Upvotes: 0
Received 0 Upvotes on 0 Posts
If they wanted to do that, they should have placed the GFCI as the next receptacle and just used a none GFCI for the fridge.
 
  #10  
Old 09-22-11, 09:58 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Is it possible the previous owner intentionally wired it backwards so if it was unknowingly tripped the food in the refrigerator wouldn't spoil?
There would be better ways to do that. Probably just a mistake. The new generation of GFCI receptacles will not turn on at all if they are wired backwards. It's more like a design flaw in the older style that it will seem to work when wired wrong.
 
 