100 AMP Sub Panel?
Old 09-24-11, 12:50 PM
100 AMP Sub Panel?
I am having an electric in floor heat boiler installed and I am trying to do as much wiring as I can. The boiler is rated at 75 amps, but has two breakers on the panel, a 50 amp and a 60 amp. I would like to install a sub panel off the main panel to power the boiler, both main and sub are in the basement, about 60 feet apart.
Looking at the boiler I would assume 110 amps would be required, but the documentation says the rating is only 75 amps.
My question is, can I get by with a 100 amp sub panel with a 90 amp main breaker? In other words, do I go by the boiler specifications or the physical breakers in place to size this thing?
Old 09-24-11, 05:24 PM
CasualJoe's Avatar
My opinion is you need a 100 amp subpanel fed from a 100 amp breaker in the main service panel.
Old 09-26-11, 09:09 AM
The circuit for a load like a boiler is usually sized for 125%, so 75A * 125% = 94A. You should do a 100A panel with full 100A feeder. That means #3 copper in conduit, #2 copper cable NM or SER, #1 aluminum in conduit, or #1/0 aluminum SER cable.