Convert 3-wire circuit to 2-wire?
Old 10-02-11, 10:31 PM
C
Hello,
I have a 220v oven outlet fed by 8/3 NMb. I wish to convert the outlet to a 15 amp single pole circuit. Is it permissible to 1) Replace the 40A dual breaker with a 15A single pole breaker; 2) connect only the black wire to the 15A breaker; 3) connect the other end of the black wire to the 15A outlet; 4) cap off both ends of the red wire in the 8/3, since it would no longer be used?
Old 10-02-11, 10:42 PM
ray2047's Avatar
Received 13 Votes on 11 Posts
Yes, if you have a black, white ,and bare. You will have to wire nut smaller gauge pigtails for the breaker and the receptacle. Since you have #8 I would suggest a 20 amp breaker. The #8 may even fit a 20a breaker without a pigtail.
Old 10-03-11, 04:20 AM
chandler's Avatar
Received 6 Votes on 6 Posts
To add, on the receptacle end, you will most likely need to use a 4x4 box with a plaster ring reducing it to a single receptacle. The #8 wires (all 3) will need to be in that box, along with your pigtails, and it may get cramped in a 2x4 box.
Old 10-03-11, 03:14 PM
Justin Smith's Avatar
I would use a 2-pole breaker and use it as a multiwire circut. If the receptacle is on the counter it will need gfci protection.
A 20A breaker should be rated for up to #8.
Old 10-03-11, 06:39 PM
CasualJoe's Avatar
Received 92 Votes on 82 Posts
I think that would be up to the different manufacturers, but I do know a Square D QO or QOB series breaker, 10-30A will accept (1) 14-8 AWG Al/Cu OR (2) 14-10 AWG Cu. I wouldn't bet on all 20 amp breakers accepting conductors larger than #10 just like I wouldn't bet on all manufacturer's breakers accepting 2 conductors.
Old 10-03-11, 08:19 PM
Thats the model I had in my hand. Cutler-hammer's br takes up to 8 as well as GE.
Old 10-04-11, 07:56 AM
belgarid's Avatar
When looking at breakers they need to be the same manufacturer as the panel. You can't use another manufacturer’s breaker just because it has the features you are looking for.