Extra 240v circuits - what to do?
Old 10-03-11, 06:45 PM
In my utility room there is an electrical box with a blank cover.
Inside are three conductors - a red, black and white. All three conductors looks like either #10 or #12. The wires are capped with wire nuts not connected to anything.
The red goes back to a 30A breaker. The black goes to another 30A breaker. The panel label for these two circuits says "Kiln". I guess there used to be a kiln may be for pottery or clay?
I am wondering if I could use these two circuits for something else? Besides having extra dryer?
Old 10-03-11, 07:22 PM
Justin Smith's Avatar
I would put in a 2-pole 20A breaker and install 2 gfci's in the box. Now you have 2 20A circuts to plug in whatever.
Old 10-03-11, 07:48 PM
Is there a ground wire or metal conduit between the box and the breaker panel?
Old 10-03-11, 08:01 PM
There is a EMT conduit between the box and the panel. There is also a green ground wire screwed into the metal box.
Old 10-04-11, 05:18 AM
pcboss's Avatar
You can repurpose that circuit. You would need to check if GFI protection is required for that area. You may also need to pigtail a smaller wire onto each to allow the conductor to fit the devices. A breaker change may be required.
General purpose circuits are limited to a 20 amp max.
Old 10-04-11, 06:18 AM
ray2047's Avatar
If you reduce the breaker size to 20a for a multi-wire 120v circuit be sure you use a 2 pole breaker not two single pole breakers as you seem to indicate you now have.