Fridge and dishwasher: 20A required?

Reply

  #1  
Old 10-27-11, 08:21 AM
Member
Thread Starter
Join Date: Dec 2009
Location: Virginia
Posts: 158
Fridge and dishwasher: 20A required?

On both my DW and Fridge, the manuals say 15 or 20 amp circuit, dedicated.

DW is a Kitchen Aid, KUDE50XXX (newer model, but still heated dryer)
Fridge is a Kitchen Aid 42" built in, has a label that says 8.5A peak load.

The fridge I'm not as worried about since 8.5A is well below the 12A 80% limit on a 15A circuit.

Not sure about the DW. It doesn't say its current draw.

The reason I ask is that I just ran out of 12-2 and have 150' of 14-2 left.

Any requirements for 20A on either of these circuits? Or does the manual trump NEC? I'll do what's required, but I want to do my homework first.

Thanks,
Anthony
 
Sponsored Links
  #2  
Old 10-27-11, 08:28 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,357
The NEC states any instructions must be followed. If the instructions offer you the option of either the 15 or 20 you are fine with the 15 amp circuit.
 
  #3  
Old 10-27-11, 08:32 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,295
Originally Posted by arc2v View Post
The reason I ask is that I just ran out of 12-2 and have 150' of 14-2 left.
It would be okay to do dedicated 15A circuits to each appliance. Dishwashers are usually in the 10-12A range when they have a heat cycle. I have never seen a residential model that required greater than a 15A circuit.

Or does the manual trump NEC? I'll do what's required, but I want to do my homework first.
The manual generally trumps NEC.
 
  #4  
Old 10-27-11, 10:11 AM
Member
Thread Starter
Join Date: Dec 2009
Location: Virginia
Posts: 158
Thanks guys, I appreciate the help.
 