URD in conduit

Planning on running AL 2-2-2-4 for a feed to an outbuilding from my house. Does the exposed cable inside my basement......ie from the panel to the exterior wall, need to be in conduit. I plan to run PVC once outside. Thx
 
Sponsored Links
  #2  
Old 11-17-11, 10:58 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
URD (underground residential distribution) cable cannot be installed indoors at all. It does not have a fire retardant coating. You'll have to put a junction box on the exterior wall of the house and use SER cable or conduit with THHN or XHHW conductors pulled.
 
  #3  
Old 11-17-11, 05:53 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,239
Received 40 Votes on 32 Posts
I plan to run PVC once outside.
You can do that, but there is really no need for the extra expense of URD if it will be in conduit.
 