8 GA wire for clothes dryer


  #1  
Old 11-23-11, 03:50 PM
T
Member
Thread Starter
Join Date: Nov 2001
Location: CANADA
Posts: 298
Received 0 Votes on 0 Posts
8 GA wire for clothes dryer

I am relocating a clothes dryer, and the existing outlet is too far away to be used, and there is not enough wire to re-route to where the new outlet will be.

I have some 8 GA wire left over from a previous job that is long enough, so I want to use it rather than buy some new 10 GA.

I just want to confurm that there are no problems doing this (and connecting to current 30A breaker).

Also want thoughts of surface-mounting a junction box and adding the extra 10' of 8 GA wire needed.

I presume the first choice is better (safer?).

Thanks for your help!
 
  #2  
Old 11-23-11, 05:37 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
#8 is fine but:
What kind of wire? Do you mean cable not wire? If cable it must be 8-3 plus ground. Is the dryer receptacle 3-wire or 4-wire? A 3-wire circuit can not be extended.
 
  #3  
Old 11-23-11, 05:46 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,126
Received 348 Votes on 301 Posts
Also, is it copper or aluminum wire?
 
  #4  
Old 11-23-11, 06:09 PM
T
Member
Thread Starter
Join Date: Nov 2001
Location: CANADA
Posts: 298
Received 0 Votes on 0 Posts
Details

It's 3 wire (copper) with ground. NMD90, if I recall correctly (not at hand).
 
  #5  
Old 11-24-11, 04:48 AM
W
Member
Join Date: Feb 2006
Location: USA
Posts: 6,784
Received 34 Votes on 31 Posts
Wire Gauges

I would not mix wire gauges in the same branch circuit.
 
  #6  
Old 11-24-11, 06:13 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Originally Posted by TomLusk View Post
It's 3 wire (copper) with ground. NMD90, if I recall correctly (not at hand).
But is the original circuit 4-wire or 3 wire?

Replies based on US code but Canadian should be similar.
 
  #7  
Old 11-24-11, 08:02 AM
T
Member
Thread Starter
Join Date: Nov 2001
Location: CANADA
Posts: 298
Received 0 Votes on 0 Posts
Hi Ray:

The original circuit is 3 wire red/white/black plus ground. New is the same.

Tom
 
  #8  
Old 11-24-11, 08:20 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,823
Received 111 Votes on 98 Posts
The original circuit is 3 wire red/white/black plus ground. New is the same.
That would be considered a 4 wire circuit. You can extend it for your dryer with additional #8 or #10 NM cable as long as it is protected by no more than a 30 amp breaker. Although it isn't always adviseable to mix wire sizes, it wouldn't be a code violation. As Ray stated


Replies based on US code but Canadian should be similar.
 
 