Can I add an outlet to existing circuit running to jet tub?
#1
Member
Thread Starter
Join Date: Nov 2011
Location: Canada
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Can I add an outlet to existing circuit running to jet tub?
I am attempting to replace the last of the knob and tube wiring in an older house and because a previous owner installed a jet tub right in the way I can't get at the old wire running to the bathroom outlet. It would be very easy to tie the outlet into the wire powering the jet tub. The jet tub motor is rated at 9.8 amps and it is on a dedicated 15 amp circuit with 14-2 wire. The jet tub would never be used while the plug is being used. However I realize there may be safety issues over and above the 12 amp rule dictating a dedicated circuit for the jet tub. Can I safely make the connection?
THanks
Doug
THanks
Doug
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
No. A jetted tub requires a dedicated circuit. Also, at least in the US, a bathroom receptacle must be on a 20 ampere circuit and that circuit can only feed bathroom receptacles (multiple bathrooms) or the receptacle, light(s) and exhaust fan in a single bathroom.
I suspect Canadian code is the same in this area.
I suspect Canadian code is the same in this area.
#5
Member
Thread Starter
Join Date: Nov 2011
Location: Canada
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Unfortunately it's an 85 year old 1&1/2 story with no way of doing anything easy or even with moderate difficultly. If whoever put in the jet tub had replaced the K&T during the construction it wouldn't have been a problem but now it would take ripping out the floor at the very least. Moral to the story is when doing a renovation on an old house think about it and do it right.
Thanks
Doug