Iím rewiring for a new range. Instead of buying a cord (that doesnít come with it) and a new outlet, why canít I run the wire thru the box, use some kind of stain relief faceplate and hard wire into the range?
 
Sponsored Links
  #2  
Old 11-25-11, 07:02 AM
Member
Join Date: Oct 2008
Posts: 1,312
Solid wire is not designed to be moved. Bend it back and forth so many times, then it will break like a coat hanger.

Appliance cords are designed to be moved as they use stranded wire. So ok to move the appliance for cleaning under it. Also with a plug you can unplug the range and move it out of the way to install a new floor or whatever.

Also think about the future. If at some point you are no longer around and someone else in your family needs to get a new range, they might have to hire an electrician to install an outlet. Or if you sell the house, a home inspector would surely write that up as something which needed fixing. And at that point in the sale, you might be required to have a licensed electrician do the work. A lender or FHA might require that.

For example I have seen wording like this for loans...
"All repairs/work must be completed within (6) months of the closing date. Repairs must be completed by a contractor unless the borrower can demonstrate the required expertise/experience (ie: plumbing repairs would require a licensed plumber, electric work would require a licensed electrician)."
OR mortgages : OR mortgage rates and home loans
 
  #3  
Old 11-25-11, 07:27 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,631
Why don't you want to use a cord set and receptacle?

The reason they don't come with a cord set is because there are two different types of receptacles the purchaser might have and the manufacturer can't know which.
 
  #4  
Old 11-25-11, 10:50 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,356
Originally Posted by ray2047 View Post
The reason they don't come with a cord set is because there are two different types of receptacles the purchaser might have and the manufacturer can't know which.
I don't agree. Back when there was only one standard for cord/receptacle the manufacturers STILL didn't include the cord. They never did (and still don't) on electric clothes dryers either. I think it is a practice that once started is all but impossible to break.

I have found that the cordset IS a negotiable item when purchasing new equipment so while a new receptacle may be needed you can get the cord supplied by the appliance retailer.

One more thing...I'm pretty sure that except for a "fixed in place" (i.e. built-in) appliance the National Electrical Code requires a means to disconnect the appliance from the electrical supply. The cord and receptacle arrangement is the least expensive and easiest.
 
  #5  
Old 11-25-11, 01:36 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,350
A disconnect would also be required for a fixed in place appliance that was hard wired. The cord and plug can serve as the disconnect for the stove.
 
  #6  
Old 11-25-11, 01:55 PM
Member
Thread Starter
Join Date: Jun 2005
Location: USA
Posts: 25
Thanks for the replies, I didnít think about the disconnect requirement. Iíll use a standard outlet.
 
  #7  
Old 11-25-11, 02:54 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,631
Originally Posted by Tourglide1 View Post
Thanks for the replies, I didnít think about the disconnect requirement. Iíll use a standard outlet.
Just remember you will need a total of four wires, ground wire*, two hots and a neutral. Three wire is no longer code compliant. #8 for 40 amp and #6 for 50 amp. Use a NEMA 14-50 receptacle for both 40a and 50a.

*If metal conduit is used uninterrupted to the breaker box and a metal junction box for the receptacle code doesn't require a ground wire but it is a good idea.
 