Electric furnace wire/breaker size
Old 11-28-11, 12:38 PM
N
I am installing a used electric furnace (RUUD) htr. K.w. 10.8/14.4. Amps 55.3/63.4. Mca 69.2/79.3. Mop 70/80. It came with 2 60amp 2pole breakers connected by a jumper bar. I'm wondering what size wire to use and what breaker for the panel. Also do I need a neutral and if so would it just connect to the ground lugs. Thanks
Old 11-28-11, 06:13 PM
Tolyn Ironhand's Avatar
Received 200 Votes on 178 Posts
Since it is a 240 volt device you do not need a neutral. You do, however, need a ground which would be connected to the ground lug.
Wire size for 60 amps is #6 Copper. The ground can be #10 if you are not using a cable. (NM-b) ***Edit: See other post for amended information of wire size***
When you say there is a jumper are you talking about a handle tie or is there a set of wires between breaker one and breaker two? A picture might be helpful.
Old 11-28-11, 06:14 PM
pcboss's Avatar
Received 83 Votes on 71 Posts
MCA stands for minimum circuit ampacity. This will determine your wire size.
Depending on your voltage you may need either 70 or 80 amp conductors.
You do not need a neutral.
Old 11-28-11, 06:53 PM
CasualJoe's Avatar
Received 83 Votes on 73 Posts
What is the voltage rating of the furnace? My assumption is that this is a 240 volt furnace and you have the typical residential service voltage of 120/240 volts, is this all correct to this point? Can this furnace be connected for either KW rating, 10.8 or 14.4 or is this a two circuit furnace with both KW ratings running at the same time? The thing that bothers me is that usually having two 60 amp breakers is indicative of a two circuit 20 KW furnace, but I think what you have is a two circuit 25 KW furnace. A 25 KW furnace could be either a two or three cicuit unit. Are these breakers mounted in the furnace as a disconnecting means with the handles exposed through the top door? Can you provide a model number of the furnace?
What I suspect is this, you have a 25 KW furnace that has had a 5 KW element disconnected and one breaker has been changed to run the unit as a two circuit 20 KW furnace, but knowing the model number would probably tell the story. Once we establish exactly what you have we can tell you what size wire to run to it. I doubt you'll need a neutral conductor, just two hot wires and one ground for each circuit.
Old 11-28-11, 07:50 PM
F
Received 35 Votes on 27 Posts
OR, those posted specifications may be for a 208/240 furnace. The "...2 60amp 2pole breakers connected by a jumper bar." could be a two-pole circuit breaker and the OP doesn't know the difference between that and two single-pole breakers.
At any rate, the NEC requires that fixed heating appliances have their branch circuit designed for 125% of full load current. That would point to #4 copper conductors and an 80 ampere branch circuit breaker as is also specified by the MCA and MOP numbers.
Old 11-29-11, 08:06 AM
N
More details: RUUD Model # UBHA-17J15SUCA, Volts: 208/240vac
HTR. K.W. : Total=10.8/14.4, Mult. Suppl. Circuit Data=CKT#1-7.2/9.6, CKT#2-3.6/4.8
Amps: Total=55.3/63.4 Mult. Suppl. Circuit Data=CKT#1-38/43.4, CKT#2-17.3/20
MCA: Total=69.2/79.3 Mult. Suppl. Circuit Data=CKT#1-47.5/54.3, CKT#2-21.7/25
MOP: Total=70/80 Mult. Suppl. Circuit Data=CKT#1-50/60, CKT#2-25/25
The breakers are accesable as a shut-off on the panel door. They are connected by a bus bar with lugs to connect both breakers through one set of wires "single point wiring"
thanks for your help.
Old 11-29-11, 02:53 PM
Ok, That makes more sense now. You need to wire it as the others have mentioned using the MCA and the MOP. This will require #4 copper and a maximum breaker or fuse of 80 amps @ 240 volt.