I was preparing to replace an overhead light and noted that I have 57V across neutral and hot wires when the light switch is turned off; 120 when on. I checked other switched outlets on separate circuits in the house and found the same situation. I stripped the panel of all circuits except for the one in question and I still have voltage. I thought I might have a ground somewhere backfeeding power. The only way to get to zero volts is to open the breaker for the circuit I am testing. Same thing for the other two I checked. Why why why? Do I have three separate problems or one common?
#3
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 4
Received 0 Votes
on
0 Posts
Yes on the digital. This sparks a vague memory of something I once knew. How do I test using a simplified method and without special meters to make sure I am just seeing ghost voltage? I
#4
Do you have a two lead tester that is used to plug into outlets to check for voltage?
Another is with the power on, turn the light on. Then turn off the breaker that controls the circuit for the light. Without touching the position of the switch (on), check for voltage using the digital meter. This places a load on the line and you should now get a zero reading.
The other option is if there are any outlets on the same circuit is to plug in a lamp and turn it on. This also places a load on the circuit that will drain the ghost voltage.
Another is with the power on, turn the light on. Then turn off the breaker that controls the circuit for the light. Without touching the position of the switch (on), check for voltage using the digital meter. This places a load on the line and you should now get a zero reading.
The other option is if there are any outlets on the same circuit is to plug in a lamp and turn it on. This also places a load on the circuit that will drain the ghost voltage.
#5
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 4
Received 0 Votes
on
0 Posts
Do you have a two lead tester that is used to plug into outlets to check for voltage?
Another is with the power on, turn the light on. Then turn off the breaker that controls the circuit for the light. Without touching the position of the switch (on), check for voltage using the digital meter. This places a load on the line and you should now get a zero reading.
The other option is if there are any outlets on the same circuit is to plug in a lamp and turn it on. This also places a load on the circuit that will drain the ghost voltage.
Another is with the power on, turn the light on. Then turn off the breaker that controls the circuit for the light. Without touching the position of the switch (on), check for voltage using the digital meter. This places a load on the line and you should now get a zero reading.
The other option is if there are any outlets on the same circuit is to plug in a lamp and turn it on. This also places a load on the circuit that will drain the ghost voltage.
#6
If you get a reading of zero volts with the breaker open you should be safe. Leave the breaker open when replacing the light. You may also want to place a peace of tape across the breaker with a note to make sure no one turns the breaker back on.
When you are testing with the breaker closed (power to circuit) you can still be picking up ghost voltage that is generated in the lines after the switch with no load on those lines. If you connect the new light you should get a reading of zero as it will now place a load on the circuit and dissipate the ghost voltage.
When you are testing with the breaker closed (power to circuit) you can still be picking up ghost voltage that is generated in the lines after the switch with no load on those lines. If you connect the new light you should get a reading of zero as it will now place a load on the circuit and dissipate the ghost voltage.
#9
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 4
Received 0 Votes
on
0 Posts
I went back today and hooked up a light and measured across it with the switch off... 0 volts. So if I dig out my old analog meter I wouldn't see the ghost voltage?