too much on 1 circuit or is this ok

Reply

  #1  
Old 12-01-11, 04:15 PM
D
Member
Thread Starter
Join Date: Sep 2011
Location: USA
Posts: 71
Received 0 Votes on 0 Posts
too much on 1 circuit or is this ok

Should I split these into 2 circuits or is having all this on 1 15amp circuit ok?

70cfm bath fan w/ light - 2amps
Hardwired smoke detectors (5) - 0.04amps each
Bath room lights - 2amps
Hallway lights - 1amp
1 receptacle in hallway
 
Sponsored Links
  #2  
Old 12-01-11, 04:26 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
So long as you have a separate dedicated 20a receptacle circuit for the bathroom(s) that is okay.
 
  #3  
Old 12-01-11, 04:40 PM
D
Member
Thread Starter
Join Date: Sep 2011
Location: USA
Posts: 71
Received 0 Votes on 0 Posts
Originally Posted by ray2047 View Post
So long as you have a separate dedicated 20a receptacle circuit for the bathroom(s) that is okay.
Yup separate gfci protected circuit for bathroom outlets.
 
  #4  
Old 12-02-11, 04:18 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Received 0 Votes on 0 Posts
Yup separate gfci protected circuit for bathroom outlets.
Then you're good!
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: