I was reading the code and I don't under stand what derating is and how it applies.

Why is it allowable to derate neutral, relative to the line wires?
 
  #2  
Old 12-11-11, 05:07 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Derating is a compensation for the inability to radiate heat because the cables or wires are close together or are in a high heat area. The ampacity is reduced.

The neutral is sometimes allowed to be smaller than the ungrounded conductors due to not all circuits need a neutral.
 
  #3  
Old 12-12-11, 07:28 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 6,095
Received 422 Upvotes on 375 Posts
Typically, you only have to be concerned with derating if you're running more than 9 current carrying (hot & neutral) wires in one channel (usually conduit). When you pull NM-B through studs/joists, you want to limit it to no more than 3 (or 4) cables through a single hole across a few studs or joists.
 
 