Still messing with the welder circuit
Well, I got it connected. Is this right? I am still not quite understanding the seperate ground bar. Isn't he power reaching the main panel in the house now through the ground. This is a detachd building. thanks
[IMG]
[/IMG]
[IMG]

Last edited by mikerallye; 12-21-11 at 09:19 AM. Reason: pics
#2
In a nut-shell, the reason sub-panels grounds and neutrals are kept separate is to keep current from flowing on the ground wire. In normal operations, a neutral is a current carrying conductor, a ground wire is not. Any connection between neutral and ground after the main disconnect panel would cause all grounded (bonded) paths to become energized…ground wires of branch/feeder circuits, metal boxes and equipment, gas and water pipes, ductwork, siding, etc. Though electricity takes the path of least resistance, it will take all paths it can to get back to its source.
Installing a sub-panel is much like installing a metal junction box. The fourth wire brought in to feed the sub-panel (the ground wire) is merely an equipment ground wire, and acts the same as found in a metal junction box for a branch circuit. It bonds the sub-panel enclosure, and (by using a separate ground bar) gives a place to land the grounds for the branch circuits leaving the sub-panel, and to keep them separate from the neutral.
Installing a sub-panel is much like installing a metal junction box. The fourth wire brought in to feed the sub-panel (the ground wire) is merely an equipment ground wire, and acts the same as found in a metal junction box for a branch circuit. It bonds the sub-panel enclosure, and (by using a separate ground bar) gives a place to land the grounds for the branch circuits leaving the sub-panel, and to keep them separate from the neutral.
#4
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 22
Received 0 Votes
on
0 Posts
Thanks for clarifying that. Now, the 60 amp upper right breaker is the welder circuit. this is correct isn't it? Will the ground wire be ok like it is or is there a better way to do this? The ground is not engerizing anything like it is? thanks