New bath electrical

I'm running wire for a new bathroom. I have a dedicated 240v for a baseboard heater and another 120v for lights and some wall recepticles. Now I want to run a line for 2 double gfci plugs over the vanity and then continue to run the line to a fan/light/night light unit over the shower. This unit can be placed over the shower as long as its protected by a gfci. The wire from the first gfci to the second gfci will be pigtailed so the second will not be reliant on the first. The fan/light unit will be protected by the second. So a wire coming from the load side will go to the 3 way switch that controls the fan unit. I'm using 12/2 from the fuse box to the first gfci and 12/2 from the first gfci to the second. Can I then run a 14/2 from the second gfci to the 3 way switch then 14/2 to the fan unit? Or do I have to continue with 12/2 to the 3 way switch which controls the fan unit. The fan unit does not have a heater and is a 15 amp unit.
 
Sponsored Links
  #2  
Old 12-29-11, 11:50 AM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,513
Received 89 Votes on 78 Posts
20 amp circuit needs 12 ga wire.
 
  #3  
Old 12-29-11, 11:55 AM
S
Member
Thread Starter
Join Date: Dec 2011
Location: canada
Posts: 2
Received 0 Votes on 0 Posts
Can I change gfci's to 15 amp and still use the 12/2 with a 15 amp breaker?
 
  #4  
Old 12-29-11, 12:12 PM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,513
Received 89 Votes on 78 Posts
Wait for one of the pros to chime in, this may need to be a 20 amp circuit.
 
  #5  
Old 12-29-11, 09:56 PM
D
Member
Join Date: Aug 2011
Location: USA
Posts: 62
Received 0 Votes on 0 Posts
I'm definitely not a pro, but I believe it does need to be a 20A circuit. This would mean you have to use 12ga wiring, not 14ga. NEC 210.11(C)(3) states:

Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.

Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
 
  #6  
Old 12-30-11, 06:05 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,082
Received 63 Votes on 55 Posts
This needs to be #12 on a 20 amp circuit.
 
  #7  
Old 01-02-12, 07:12 PM
palmcoast's Avatar
Member
Join Date: Dec 2006
Location: New Jersey
Posts: 107
Received 0 Votes on 0 Posts
I also thought you would not be allowed to have recepticals and lighting on the same circuit?
 
  #8  
Old 01-03-12, 06:04 AM
C
Member
Join Date: Jul 2009
Location: SE Iowa
Posts: 83
Received 2 Votes on 2 Posts
You can, so long as they serve the one bathroom only.
 

Last edited by pcboss; 01-03-12 at 11:38 AM. Reason: added one for clarity.
  #9  
Old 01-03-12, 03:45 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,044
Received 78 Votes on 73 Posts
As others have said, the circuit needs to be 20A and therefore needs to be 12ga wire.

Also, I see no reason in wasting $10 on a second GFI. Of course, there's nothing code-wise wrong with your plan, but there's no reason you can't have one GFI receptacle that protects the downstream receptacle and light/fan
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: