CAT-5 for doorbell?l

I already have a roll of CAT-5 cable at home, can I use this for a new doorbell install?
 
  #2  
Old 01-02-12, 09:25 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Sure. I always twin a pair for each conductor. Example: blue/blue-white twisted together as a single conductor and red/red-white twisted together as the second conductor.
 
  #3  
Old 01-03-12, 10:57 AM
W
Member
Join Date: Apr 2006
Location: USA
Posts: 133
Received 0 Votes on 0 Posts
Not if you are using 120 volts. 12, 24 v is OK.....
 
  #4  
Old 01-03-12, 11:42 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,254
Received 114 Votes on 99 Posts
I would run regular thermostat wiring. Phone cable is only 24 gauge.
 
  #5  
Old 01-03-12, 02:57 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,541
Received 0 Votes on 0 Posts
I would run regular thermostat wiring. Phone cable is only 24 gauge.


Read more: http://www.doityourself.com/forum/ne...#ixzz1iRzjPkOu
I thought 24AWG was good for 1 amp? (at 24v)
 
  #6  
Old 01-03-12, 04:51 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,254
Received 114 Votes on 99 Posts
I was looking at it from a voltage drop perspective. When you only start out at 12 volts it is critical to minimize your loses.
 
  #7  
Old 01-03-12, 06:57 PM
A
Member
Join Date: Oct 2005
Location: Milwaukee WI
Posts: 1,339
Received 0 Votes on 0 Posts
I've run into a couple of situations where I've thought fusing the secondary on the transformer would have been a good idea to protect the downstream wire, which is typically 18 AWG. That would be even more of a concern with 24 AWG.

One 24 AWG conductor has a cross-sectional area of 0.205 sq mm, so two would be 0.410, right? That's the same as 21 AWG. 18 AWG is 0.823 sq mm.

For my doorbell wiring I used 16 AWG, which is 1.31 sq mm.

Questions for somebody with more knowledge:

1. If the (30, 40, or 50VA) doorbell transformer is shorted at the far end of the secondary circuit, what AWG wire is needed to allow the unfused secondary of the transformer to fry itself, without damaging the conductors & insulation of the secondary circuit?

2. What size fuses should protect 24, 22, 20, 18, and 16 AWG?

Area source:
https://en.wikipedia.org/wiki/American_wire_gauge
 
  #8  
Old 01-03-12, 07:53 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,819
Received 108 Votes on 95 Posts
I believe regular bell wire used to be available, but most often I used to see 18 gauge thermostat cables used for door bell wiring.
 
  #9  
Old 01-05-12, 07:51 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,481
Received 134 Votes on 123 Posts
Choose a fuse for the transformer secondary to match the output of the transformer, for example a 50 va transformer with a 24 volt output will deliver 2 amps so use a 2 amp fuse.
 
 