Restaurant power supplys

Reply

  #1  
Old 01-06-12, 08:10 AM
Member
Thread Starter
Join Date: Dec 2011
Location: USA
Posts: 17
Restaurant power supplys

Hi everyone,

I was wondering if anyone can tell me what are the typical
power supplies found in restaurants ? for example, do all restaurants have 208v 3 phase outlets or 460v 3 phase?

thanks in advance,
jason
 
Sponsored Links
  #2  
Old 01-06-12, 01:23 PM
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
The most practical system for a resturant is 3-phase , 4-wire , 120 / 208 volts. This provides---

120 volt 2-wire circuits for liting , receptacles , 120 volt appliances, and 120 volt single-phase motors.

208 volt 2-wire circuits for for 2-wire 208 appliances and 208 volt single-phase motors

120/208 volt 3-wire circuits for 3-wire 120 / 208 appliances

208 volt 3-wire circuits for 3-phase motors.
 
  #3  
Old 01-06-12, 03:54 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
What's used around here is:
120Y208
120/240V Delta (most common)
120/240V Single Phase
480Y277V
240Y416 (no clue why)
 
  #4  
Old 01-06-12, 06:39 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,383
I was wondering if anyone can tell me what are the typical
power supplies found in restaurants ?
I don't think there is such a thing as "Typical" in this case. You might find almost any voltage in a commercial kitchen. Some times you may find 480 volt air-conditioning, refrigeration and even coffee makers as well as 277 volt fluorescent lighting. I think the ideal would be 120/208 volt 3P4W for most small to medium size restaurants. That being said, I have also seen older restaurants with two services, a single phase service and a 240 volt Grounded "B" Phase 3 phase service.
 
  #5  
Old 01-07-12, 01:42 AM
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
I am on the same page as Joe is there is no specfic voltage requirement in the resuarant.

Now for the uilziation of the incomming power source will varies a bit depending on the POCO grid and what they will provide the supply to the place.

And service size will varies a bit as well they can be anywhere from single phase 120/240 volt 200 amp and up plus three phase service will typically go 400 amp and up depending on the layout and power requirement of that restuarnt.

I just have one done not too long ago by using the European specs that place have 630 amp service 415Y240 volt system

PATTBAA.,

I know you say "208 volt 3-wire circuits for 3-phase motors."

There is also a 208 3 Ph water heaters as well it a pretty common item if you have three phase power avaiable.

Justin.,
240Y416 (no clue why)
I will give you a straight answer that voltage is common used in European area., 415Y240 is proper term.

Merci,
Marc
 
  #6  
Old 01-07-12, 06:57 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,383
Very good answer, Marc. If you are thinking of opening a restaurant, the important thing is to find out what service the POCO will provide you and give this information to the engineer designing your restaurant so the proper electrical system can be designed for the equipment. By all means, don't buy any equipment without consulting the POCO and engineer on the job as it all must have the proper voltages specified.
 
  #7  
Old 01-07-12, 07:11 AM
Member
Thread Starter
Join Date: Dec 2011
Location: USA
Posts: 17
Restaurant power supplies

Thanks guys,

I'm in the drain cleaning business and have been looking at a piece of equipment that requires 3ph/460v. so now i know i can't rely on having adequate power being available.

thanks again,
Jason
 
  #8  
Old 01-07-12, 07:23 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,277
You can pretty much make what ever voltage you need using transformers. Of course this will add to the cost of the equipment.
 
  #9  
Old 01-07-12, 07:51 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,383
Originally Posted by Jason421 View Post
Thanks guys,

I'm in the drain cleaning business and have been looking at a piece of equipment that requires 3ph/460v. so now i know i can't rely on having adequate power being available.

thanks again,
Jason
I have no idea what type of drain cleaning equipment would require 3 phase, but if it is also available in single phase 240 volt, I'd go that route. Even if a restaurant is supplied from the utility with a 277/480 volt service, you can be assured there will be a transformer providing 120/208 volt 3 phase service or single phase service within the restaurant too (to provide for 120 volt receptacles) and that either of those services would operate a 240 volt single phase piece of equipment.
 
  #10  
Old 01-07-12, 07:51 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,043
I'm in the drain cleaning business and have been looking at a piece of equipment that requires 3ph/460v. so now i know i can't rely on having adequate power being available.
And you can't rule out a small food establishment having only 120/240 single phase power with no good way to plug into 240v. If that equipment is really what you need best also consider a truck mounted generator, maybe powered by a PTO.
 