Recommended AWG for 60 AMP Circuit
I want to run a new 60 amp circuit for a hot tub. The Maximum Current Draw (according to the manufacturer) is 48 amps. The run is about 100 feet. I was thinking of running four 6 AWG THHN wires in a 3/4" EMT conduit (2 hots, 1 neutral, and 1 ground). The run will start at the circuit panel and terminate at the outdoor GFCI, which will then run about 10 feet to the hot tub.
Is 6 AWG THHN large enough, or should I go with 4 AWG THHN in 1" EMT?
Thanks in advance.
Is 6 AWG THHN large enough, or should I go with 4 AWG THHN in 1" EMT?
Thanks in advance.
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Number 6 copper should be fine. Voltage drop will be under 2%, about 4.6 volts. Be sure that the conductors are rated THHN/THWN rather than just THHN. The W means weatherproof and is necessary whenever conduit is buried or located outside.
#3
I was thinking of running four 6 AWG THHN wires in a 3/4" EMT conduit (2 hots, 1 neutral, and 1 ground). The run will start at the circuit panel and terminate at the outdoor GFCI, which will then run about 10 feet to the hot tub.
#4
Member
I would use at least 1", maybe 1-1/4". It's a lot easier than using all that lube and trying to get through any bends and push slack through conduit bodies.