Overhead wire for 200 amp service from meter to panel
#1
Member
Thread Starter
Join Date: Mar 2012
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Overhead wire for 200 amp service from meter to panel
I just bought a rundown house that was built in the early 70's. The meter has 200 amp service on a pole about 60 feet from the house. This service is split into two 100 amp services. One goes to the house and one to a workshop. The 100 amp services are underground in 1.5" conduit, 2 hots and a ground, no neutral. I want to upgrade the panel in the house for the entire 200 amp service, and then have a separate service installed in the work shop.
I want to run the 4/0 aluminum to the house from the meter overhead because the small conduit is a PITA. My question is what type of wire do I need to go from the meter to the house overhead. I know it needs to be water and sunlight resistant, XHHW? and I've read about messenger wire to carry the weight, but I don't know exactly what I'm looking for.
I've wired many subpanels within a building, but never done anything overhead. I'll also be needing two service heads. How are they sized? Is there a particular type that I need? Also, is there a basis for how much slack to leave in the run, and how to account for it when measuring for wire length?
Thanks
I want to run the 4/0 aluminum to the house from the meter overhead because the small conduit is a PITA. My question is what type of wire do I need to go from the meter to the house overhead. I know it needs to be water and sunlight resistant, XHHW? and I've read about messenger wire to carry the weight, but I don't know exactly what I'm looking for.
I've wired many subpanels within a building, but never done anything overhead. I'll also be needing two service heads. How are they sized? Is there a particular type that I need? Also, is there a basis for how much slack to leave in the run, and how to account for it when measuring for wire length?
Thanks
#2
The meter has 200 amp service on a pole about 60 feet from the house.
This service is split into two 100 amp services.
Your post was not clear. Can you clear up some details?
#3
I took it as the service is on the pole, but then feeds 2 100 amp panels remote from the pole.
Depending on the loads the OP may be looking at a 320 service with 200 to the house and a 100 to an outbuilding.
Depending on the loads the OP may be looking at a 320 service with 200 to the house and a 100 to an outbuilding.
#5
Member
Thread Starter
Join Date: Mar 2012
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Meter is on the pole and has two 100 amp main breakers, no 200 amp main. Panel is in the house. I want to change the 100 amp panel in the house to a 200 amp service from the meter at the polewith a 200 amp main breaker, new wire, ground, and panel. I will scrap the other 100 amp service to the shop and install a brand new service there that is in no way connected the the current 200 amps. Thanks again.
#7
My first question is why do you want 200 amps to the house? Are you adding a major load such as electric hear or electric on demand water heater? IF not, then I really doubt you need 200 amps to the house. I suggest doing a load calculation to see if this is even worth doing, which I doubt it is if everything was fine before.
#8
Member
Thread Starter
Join Date: Mar 2012
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Why can you use 1/0 overhead? Is there a different table for amp ratings on overhead wiring?
As for the upgrade, I'm planning on an addition, hot tub, lot's of electronics, and I have ski tuning machines that pull some serious power.
As for the upgrade, I'm planning on an addition, hot tub, lot's of electronics, and I have ski tuning machines that pull some serious power.
#9
I suggest installing an outdoor, 200 amp panel at the pole that also has feed through lugs (square D has one that is not too much money) Otherwise you will not fine a 200 amp breaker that will connect to the stabs of a plug in buss. Then keep the 100 amp feed to the shop and run your 200 amp feed to the house.
What is serious power to you? To me it is 1000 amps or more.
Please give numbers like volts, amps/watts. Is your ski machine in the shop or the house?
I still suggest a load calc. I have a 4600 sq ft house with separate shop and barn with a 200 amp service (house had a lot of electric heat which is not gone) Doing a load calc I come up with an 80 amp load.
What is serious power to you? To me it is 1000 amps or more.

I still suggest a load calc. I have a 4600 sq ft house with separate shop and barn with a 200 amp service (house had a lot of electric heat which is not gone) Doing a load calc I come up with an 80 amp load.
#10
Forum Topic Moderator
I'll let the pros answer the wire spec questions... but you may want to confirm with the POCO that they will install a second service to your workshop. Unless it's commercial (and zoned as such), many POCOs will only install a single service to your address.
Wouldn't want to go to all this trouble and have a surprise at the end!
Wouldn't want to go to all this trouble and have a surprise at the end!
#11
I'll let the pros answer the wire spec questions... but you may want to confirm with the POCO that they will install a second service to your workshop. Unless it's commercial (and zoned as such), many POCOs will only install a single service to your address.
Wouldn't want to go to all this trouble and have a surprise at the end!
Wouldn't want to go to all this trouble and have a surprise at the end!
eyeswideopen
Why can you use 1/0 overhead? Is there a different table for amp ratings on overhead wiring?