Wiring a 50 amp 220 GFCI breaker to a 3-wire hot tub.

There is no neutral wire connection in this new hot tub. How is the GFCI breaker to be wired so it will function correctly?
 
  #2  
Old 03-27-12, 04:43 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 7,458
Upvotes: 0
Received 5 Upvotes on 4 Posts
Do you have the installation manual? Can you point us to it online?
 
  #3  
Old 03-27-12, 04:57 PM
T
Member
Thread Starter
Join Date: Mar 2012
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
  #4  
Old 03-27-12, 07:29 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,922
Received 176 Upvotes on 154 Posts
Just put the neutral tail from the GFI breaker in the neutral buss. Connect the two hots to the breaker.
 
  #5  
Old 03-28-12, 07:14 AM
T
Member
Thread Starter
Join Date: Mar 2012
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Without a neutral return from the hot tub, how does the GFI breaker detect a fault?
 
  #6  
Old 03-28-12, 10:30 AM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 19,281
Received 6 Upvotes on 6 Posts
Thats exactly what it shows in the install info Ray...they recommend THHN in conduit and show black, red and green.
 
  #7  
Old 03-28-12, 01:27 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Thats exactly what it shows in the install info Ray...they recommend THHN in conduit and show black, red and green.
Yes, that is why I'm thinking the breaker supplying the hot tub rather then the breaker at the hot tub needs to be GFCI or he needs to add a neutral but I'm waiting for the pros to confirm.
 
  #8  
Old 03-28-12, 01:52 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,922
Received 176 Upvotes on 154 Posts
The GFI will look at the outgoing power and compare it against the power that is returning on the other leg. It will function properly.
 
 