I have a dozen electric baseboard heater 20ish years old where the insulation on the return wire that goes throught the back of the heater, are failing. The wire type is TEW 105c rating the supply house doesnt carry Tew, from what I can find AWM and MTW and some THHN carry the 105c rating now in some cases.

I guess I just need to know what type of wire is being used in them now or what I can use.
 
  #2  
Old 04-03-12, 11:04 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,657
Received 2,153 Upvotes on 1,928 Posts
I would replace the heaters with new, modern units. They will not produce the same amount of heat for the same length but they operate at a lower, safer temperature.
 
  #3  
Old 04-03-12, 01:00 PM
H
Member
Thread Starter
Join Date: Apr 2012
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Well the boss wants to replace the wire the heaters are otherwise in decent condition, I personally strongly dislike baseboard electric

Ben
 
  #4  
Old 04-03-12, 04:39 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
You could order almost any type wire you need from any good supply house on 500 foot rolls, I wouldn't do it though. Are these low or high watt density heaters?
 
  #5  
Old 04-03-12, 07:05 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,272
Upvotes: 0
Received 1 Upvote on 1 Post
I'd use a wire with a high-temperature fiberglass insulation.
 
  #6  
Old 04-03-12, 07:36 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,332
Received 877 Upvotes on 740 Posts
THHN wire is only rated 90 degrees as is MTW (dry locations). See NEC table 310.13(A) (2008) for an entire list of general purpose conductors. You might also want to look at fixture wires (Art. 402) many of which have a high temp rating.
 
  #7  
Old 04-05-12, 10:19 AM
H
Member
Thread Starter
Join Date: Apr 2012
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Right although I read Southwire's THHN carries AWM rating of 105C dry.

We found 150C wire for 49 cents a foot so he is going to order that.

As far as being high density heaters, the 6 foot heaters are 1500 5 foot are 1000 and the 3 foot are 350. the ones that are the worst are the 3 foot heaters
 
  #8  
Old 04-05-12, 05:27 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
Normally low watt density heaters are 188 watts/Foot and high watt density heaters are 250 watts/Foot.
 
 