wire type in electic baseboard heater
I have a dozen electric baseboard heater 20ish years old where the insulation on the return wire that goes throught the back of the heater, are failing. The wire type is TEW 105c rating the supply house doesnt carry Tew, from what I can find AWM and MTW and some THHN carry the 105c rating now in some cases.
I guess I just need to know what type of wire is being used in them now or what I can use.
I guess I just need to know what type of wire is being used in them now or what I can use.
#2
Group Moderator
I would replace the heaters with new, modern units. They will not produce the same amount of heat for the same length but they operate at a lower, safer temperature.
#6
THHN wire is only rated 90 degrees as is MTW (dry locations). See NEC table 310.13(A) (2008) for an entire list of general purpose conductors. You might also want to look at fixture wires (Art. 402) many of which have a high temp rating.
#7
Member
Thread Starter
Join Date: Apr 2012
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Right although I read Southwire's THHN carries AWM rating of 105C dry.
We found 150C wire for 49 cents a foot so he is going to order that.
As far as being high density heaters, the 6 foot heaters are 1500 5 foot are 1000 and the 3 foot are 350. the ones that are the worst are the 3 foot heaters
We found 150C wire for 49 cents a foot so he is going to order that.
As far as being high density heaters, the 6 foot heaters are 1500 5 foot are 1000 and the 3 foot are 350. the ones that are the worst are the 3 foot heaters