Questions for rewiring a garage
Renovating my attached garage, walls are open. Using the space as part workshop, part car hole. Will fully drywall/insulate the walls when finished.
1. From a code standpoint, can I put receptacles as high or as low as I desire? (ie can I put a double gang box 3 feet off the ground to energize power tools?)
2. Since this environment will be dusty and chaotic, are there any particular plugs/plates/etc I should use?
3. I only have one 20a circuit powering the entire garage, adding another circuit would be too painful. From a code standpoint, is there a restriction on the number of receptacles I can install? Not to get too in-depth but most of the loads will only be temporary (garage door opener, attic fan, power tools) however it would be nice to spread them across 8+ receptacles for accessibility and portability, is this OK?
Any other general recommendations for workshop wiring?
Thanks.
1. From a code standpoint, can I put receptacles as high or as low as I desire? (ie can I put a double gang box 3 feet off the ground to energize power tools?)
2. Since this environment will be dusty and chaotic, are there any particular plugs/plates/etc I should use?
3. I only have one 20a circuit powering the entire garage, adding another circuit would be too painful. From a code standpoint, is there a restriction on the number of receptacles I can install? Not to get too in-depth but most of the loads will only be temporary (garage door opener, attic fan, power tools) however it would be nice to spread them across 8+ receptacles for accessibility and portability, is this OK?
Any other general recommendations for workshop wiring?
Thanks.
#2
Height is your choice. There is no limit to the number of receptacles. The receptacles need to be GFCI protected either by a GFCI receptacle as the first receptacle or a GFCI breaker. Lights do not need to be GFCI protected.
#3
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
You CAN install receptacles as high as you desire but they must be a minimum of 18 inches above the finished floor in a garage. If you have any lights that are cord-and-plug connected such as fluorescent "shop lights" utilizing receptacles in the ceiling the ceiling-mounted receptacles DO need to be GFCI protected.
I would strongly urge you to run at least one new circuit for the receptacles in order that your tools are on a different circuit than the lights. It can be dangerous to "trip" a circuit breaker feeding lighting while using your tools.
I would strongly urge you to run at least one new circuit for the receptacles in order that your tools are on a different circuit than the lights. It can be dangerous to "trip" a circuit breaker feeding lighting while using your tools.
#5
Member
Thread Starter
Join Date: Aug 2009
Location: New York
Posts: 88
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Didn't want to get into it, but I do have a 15a circuit for the lights already but I certainly will extend that circuit to the workshop lights.
One other potential problem I've come across...is there any good way to protect the romex wire while it's inside the wall? I'll be hanging A TON of stuff off the drywall so I'll probably be punching many holes. I'll put the metal-plate stud covers where appropriate but is there a decent way to protect the romex wire stapled inside to the stud? Will a simple plastic/metal conduit do?
One other potential problem I've come across...is there any good way to protect the romex wire while it's inside the wall? I'll be hanging A TON of stuff off the drywall so I'll probably be punching many holes. I'll put the metal-plate stud covers where appropriate but is there a decent way to protect the romex wire stapled inside to the stud? Will a simple plastic/metal conduit do?
#6
I would try and route the cables at heights where you are not likely to install hangers.
If you are going to use conduit it will be easier to use individual conductors.
If you are going to use conduit it will be easier to use individual conductors.
#7
I do have a 15a circuit for the lights already but I certainly will extend that circuit to the workshop lights.

is there any good way to protect the romex wire while it's inside the wall? I'll be hanging A TON of stuff off the drywall so I'll probably be punching many holes. I'll put the metal-plate stud covers where appropriate but is there a decent way to protect the romex wire stapled inside to the stud?
#8
You CAN install receptacles as high as you desire but they must be a minimum of 18 inches above the finished floor in a garage.
Furd is correct. They must be above 18" in a garage. I like to put them at 48" for ease of access due to the crap that tends to get piled along walls.
Never heard of such a thing in the NEC.:NO NO NO: Unless the 2011 has it?

#10
Member
Thread Starter
Join Date: Aug 2009
Location: New York
Posts: 88
Upvotes: 0
Received 0 Upvotes
on
0 Posts
As an example, I'll be screwing a ton of shelf brackets into the studs. I didn't want to miss a stud and screw right into a cable. Obviously, using shorter screws is the best option there.
#11
I'll be screwing a ton of shelf brackets into the studs. I didn't want to miss a stud and screw right into a cable. Obviously, using shorter screws is the best option there.
Now the near edge of the cable is 2 1/8" from the face of the wall. Do you need screws longer than 2"? Those would give you 1 3/8" into the wood.
And, as pcboss commented earlier,
I would try and route the cables [for cross-wiring] at heights where you are not likely to install hangers.