wiring electrical to a sub panel outdoors
#1
Member
Thread Starter
Join Date: Apr 2012
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
wiring electrical to a sub panel outdoors
I have 2 locations in th back yard I need wiring. I ran three 8 guage wires to a barried junction box (water tight) and then I ran another three 8 guage wires from my upper patio down to the same junction box and ran the six wires total up to a conduit the Rose Garden attached to a 4x6 post how do I wire the six 8 guage wires to a sub panel.
Also on the posts on the patio and the rose garden I want to put a 4 gang outlet on the post
Also on the posts on the patio and the rose garden I want to put a 4 gang outlet on the post
#2
Were the wires installed in a conduit? If not they should have been. also for a subpanel you need 4 wires in the feeder, not 3.
Why did you run two feeders to the same box?
Why did you run two feeders to the same box?
#5
I ran three 8 guage wires to a barried junction box (water tight) and then I ran another three 8 guage wires from my upper patio down to the same junction box and ran the six wires total up to a
how do I wire the six 8 guage wires to a sub panel.
Side note: #8 AWG copper conductors are rated for up to 55 amps. That's a lot of load. Also, #8 AWG wire is too large to attach directly to 15 or 20A receptacles - but we can deal with that later.
#6
Perhaps the OP could provide more detail about their project and a better plan can be formulated. This does not sound too well thought out.
#9
You would be much better off to install a 120/240 subpanel fed with a 4 wire feeder. Twice the capacity for very little in extra cost. If you already have 6 wires to the subpanel location you can easily do this.
Check the sticky thread or search subpanels to get more info.
Check the sticky thread or search subpanels to get more info.
#11
The first thing I think of is that the #8s are too small to parallel. The would need to be 1/0 or larger.
#12
The first thing I think of is that the #8s are too small to parallel. The would need to be 1/0 or larger.
I guess it goes back to my first question.
edited to add: 120/240
Last edited by SeaOn; 04-25-12 at 04:44 PM.
#14
#15
Three wires from the subpanel to one yard location and three wires from the subpanel to another yard location would provide 120 volts to each location. For 8 gauge (anything smaller than 4 gauge) wires you must use white for neutral and green (or bare) for ground. Connect the black wire to a breaker in the subpanel, connect the white wire to the neutral bus bar and the green (or bare) wire to the ground bus bar.
For both 120 and 240 volts you would need to run a fourth wire of at least 10 gauge, green or bare. while the three 8 gauge wires are typically red black white or black black white. The pair of hot wires for each location must be connected to a double wide double breaker with handles tied togehter and positioned in the subpanel so that hot to hot measures 240 volts.
These 8 gauge wires must have breakers not exceeding 20 amps unless you have sub-subpanels out in the yard at the far ends.
(A "sub-subpanel" is wired the same way as a subpanel, i.e. with grounds and neutrals kept separate, and ground rods required. The term "sub-subpanel" is not standard.)
For both 120 and 240 volts you would need to run a fourth wire of at least 10 gauge, green or bare. while the three 8 gauge wires are typically red black white or black black white. The pair of hot wires for each location must be connected to a double wide double breaker with handles tied togehter and positioned in the subpanel so that hot to hot measures 240 volts.
These 8 gauge wires must have breakers not exceeding 20 amps unless you have sub-subpanels out in the yard at the far ends.
(A "sub-subpanel" is wired the same way as a subpanel, i.e. with grounds and neutrals kept separate, and ground rods required. The term "sub-subpanel" is not standard.)
Last edited by AllanJ; 04-26-12 at 05:34 PM.
#16
Member
Thread Starter
Join Date: Apr 2012
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thomas Mackey | Facebook
......................................................................................
......................................................................................
Last edited by ray2047; 04-26-12 at 05:39 PM.
#17
Member
Thread Starter
Join Date: Apr 2012
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks AllenJ thats what I needed to know. I tried to upload a picture but was unable to. We also need to put a grounding rod in as well.
I have 3 light poles, water sprinkler computer, pond, a fountain and a pool cover all on a single 15 amp circuit. Now they all don't run all at the same time but the possibility they could. Thats why I needed to run extra outlets so I could sever the pond and the and the foutains and have dedicated outlets.
I have 3 light poles, water sprinkler computer, pond, a fountain and a pool cover all on a single 15 amp circuit. Now they all don't run all at the same time but the possibility they could. Thats why I needed to run extra outlets so I could sever the pond and the and the foutains and have dedicated outlets.
#19
You can just splice all the conductors in the junction box once. You do not need to take them out and back in the horizontal conduit shown above.