Running electric from a subpanel

Hello guys, you have been so helpful over the past month I figured I could have another question answered by you.

I currently have a 60 amp double pole breaker in my basement feeding a subpanel in my garage. My question is, can I put in a 15 amp, 20amp, and another 20amp (all single pole) breakers from that sub panel, or do they need to be double pole since that is what the subpanel is?

Thanks in advance!
D
 
  #2  
Old 05-12-12, 09:49 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Single pole is fine in the subpanel assuming 120v circuits.
 
  #3  
Old 05-12-12, 09:51 AM
D
Member
Thread Starter
Join Date: Apr 2012
Posts: 26
Upvotes: 0
Received 0 Upvotes on 0 Posts
When you say "assuming 120v circuits" you mean on the circuits coming out from the subpanel?
 
  #4  
Old 05-12-12, 10:35 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
IF the sub-panel has a four-conductor feeder (hot, hot, neutral and equipment ground) then yes, single pole circuit breakers serving 120 volt circuits are acceptable. If the proposed circuit is 240 volts then you need to use two pole circuit breakers. If the sub-panel does NOT have a neutral conductor in the feeder then it is a 240 volt only panel and may not serve 120 volt loads. A 240 volt only sub-panel is rarely installed.
 
  #5  
Old 05-12-12, 02:33 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,933
Received 180 Upvotes on 158 Posts
The reason for the two poles is to provide the two hot legs that supply 240 volts to a circuit. A single pole breaker can only supply a 120 volt circuit.
 
  #6  
Old 05-13-12, 07:43 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,839
Received 178 Upvotes on 161 Posts
can I put in a 15 amp, 20amp, and another 20amp (all single pole) breakers from that sub panel, or do they need to be double pole since that is what the subpanel is?
Are you sure you want to attempt this? No offense intended, but you don't seem to have a clue about how electrical work is installed or how it works.
 
 