Changing ovens out with different requirements

Reply

  #1  
Old 05-20-12, 06:32 PM
Member
Thread Starter
Join Date: May 2012
Posts: 3
Changing ovens out with different requirements

I have a electric pizza oven that Im swapping out for a gas conveyor oven. The electric oven has a 50amp breaker and uses a 50 amp plug. The gas oven is rated at 15amps. Can I swap plugs and replace the 50 amp breaker with a double pole 15amp breaker. Is there any harm in this?
 
Sponsored Links
  #2  
Old 05-20-12, 07:36 PM
Nashkat1's Avatar
Member
Join Date: Mar 2012
Location: USA
Posts: 8,470
The gas oven is rated at 15amps. Can I swap plugs and replace the 50 amp breaker with a double pole 15amp breaker.
Does the gas oven need 120V or 240V?
 
  #3  
Old 05-20-12, 07:36 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,659
You'd only need a single pole breaker if the gas oven is 120v. If you are going to 120v you will need a ground wire and a white wire in addition to a hot wire. If you don't have a factory colored white and the wire is #6 or smaller you can't recolor one of the wires white (except in very limited industrial/commercial situations). Best solution if it is 120v is to just use a nearby 120v receptacle.
 
  #4  
Old 05-20-12, 07:39 PM
Member
Thread Starter
Join Date: May 2012
Posts: 3
It's needs 240 to the the blower and conveyor.
 
  #5  
Old 05-20-12, 07:46 PM
Member
Thread Starter
Join Date: May 2012
Posts: 3
The gas oven requires 240.
 
  #6  
Old 05-20-12, 07:50 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,659
You will need to reduce the hot wires at the breaker box using #14 0r #12 pigtails. Same for the new receptacle at the oven. You should not change the plug on the oven. Instead match the receptacle to the oven plug.
 