Changing ovens out with different requirements
Old 05-20-12, 06:32 PM
R
I have a electric pizza oven that Im swapping out for a gas conveyor oven. The electric oven has a 50amp breaker and uses a 50 amp plug. The gas oven is rated at 15amps. Can I swap plugs and replace the 50 amp breaker with a double pole 15amp breaker. Is there any harm in this?
Old 05-20-12, 07:36 PM
Nashkat1's Avatar
Received 6 Upvotes on 5 Posts
Does the gas oven need 120V or 240V?
ray2047's Avatar
You'd only need a single pole breaker if the gas oven is 120v. If you are going to 120v you will need a ground wire and a white wire in addition to a hot wire. If you don't have a factory colored white and the wire is #6 or smaller you can't recolor one of the wires white (except in very limited industrial/commercial situations). Best solution if it is 120v is to just use a nearby 120v receptacle.
Old 05-20-12, 07:39 PM
R
It's needs 240 to the the blower and conveyor.
Old 05-20-12, 07:46 PM
R
The gas oven requires 240.
Old 05-20-12, 07:50 PM
ray2047's Avatar
You will need to reduce the hot wires at the breaker box using #14 0r #12 pigtails. Same for the new receptacle at the oven. You should not change the plug on the oven. Instead match the receptacle to the oven plug.