Illegal, Or Just Questionable Pool Wiring?

Hello,

I started to redo the pool on the house I bought last year, and am installing a control system with a built in subpanel. After disconnecting everything that was there, I ran into something unusual.

Here is the setup

There are two breakers that feed the pool area. One is 120V 20A (hot+neutral+ground) and the other 220V 20A (2 hot + ground). They are both run in the same conduit.

My questions are,

1. Can you run two circuits in the same conduit (underground and outside)?
2. Can you ground two circuits together outside of a main breaker? They would both be grounded in the subpanel.

Steve
 
Sponsored Links
  #2  
Old 05-21-12, 05:57 AM
Member
Thread Starter
Join Date: May 2012
Posts: 11
One more thing,

The 220V circuit has a GFI breaker, but the 120V circuit just has a GFI oulet
 
  #3  
Old 05-21-12, 06:09 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 32,640
1. Can you run two circuits in the same conduit (underground and outside)?
Yes but they can't go to the same structure. Do both go to the pool

2. Can you ground two circuits together outside of a main breaker?
Code requires all grounds in a box even if from different circuits be connected together.

My suggestion would be to abandon the 120v feed and install a 120v breaker in the new subpanel. That would avoid the question of two feeds to the same location assuming the 120 feed is to the pool.
 
  #4  
Old 05-21-12, 06:14 AM
Member
Thread Starter
Join Date: May 2012
Posts: 11
The both go to the pool area. The 120V feeds a gas fired heater, some LED lights, and a few outlets in the area.

I was thinking that terminating the 120 would be cleaner. If I do that, the circuit breaker has the GFI, so I should replace the GFI outlet with a standard outlet, right?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
'