running underground coduit as opposed to uf cable

i am thinking of running underground metal conduit for my outdoor outlets and lighting. i know 125volt 20 amp or less must be 12 inches deep for uf cable but how deep should conduit be? i want to run conduit sice i may want to run future lines so i will not have to re dig. can underground conduit have regular stranded wires?
 
  #2  
Old 06-14-12, 01:47 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
i am thinking of running underground metal conduit for my outdoor outlets and lighting.
If you mean EMT it would be better to use PVC.

i know 125volt 20 amp or less must be 12 inches deep for uf cable
Only if protected by a GFCI. Otherwise minimum depth is 24"

can underground conduit have regular stranded wires?
I don't have a clue what "regular stranded wires" are but normally single conductors such as THWN are used. Either stranded or solid are available in smaller sizes. Stranded is easier to pull.
 
  #3  
Old 06-14-12, 07:51 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,868
Received 705 Upvotes on 598 Posts
You can not use EMT in the ground, you must use rigid. I agree with Ray, PVC all the way! PVC can be buried 12" if GFCI protected and 20 amps or less, otherwise it needs to be down 18". I suggest lat least running 3/4" PVC.
 
  #4  
Old 06-15-12, 04:17 AM
N
Member
Join Date: Jan 2012
Location: Canada
Posts: 2,511
Received 20 Upvotes on 18 Posts
I would definately go with 18"-24" deep, even with GFCI protection. It'll be a bit more work, but you (or a future home owner) will be less likely to hit it if you dig around it. Nothing worse then hitting the pipe with a shovel (or something else) and have to go through and replace it all.

Also, if you are thinking you might run more lines through later, Maybe run a slightly larger pipe and leave yourself a pull string (something plastic coated as to not rot).
 
 