Floor Heat wiring to GFCI breaker
I have an Easy Heat warm tiles 240 volt underfloor cable system (963 watts) with an Aube TH115 AF-240D (non GFCI) 4 wire thermostat. The floor heating cable is two wire with a braided shield. There is a two wire temperature sensor under the floor. All wires terminate in the wall at the thermostat. I would like to install a dedicated circuit for the floor heating (possibly add a towel bar heater at a later date).
1-Would a 20 amp double pole GFCI be sufficient for the load (considering that I limit the future towel bar heater to less than 10 amps) ?
2-How many conductors do I need from the panel to the t-stat?
3-Does the braided shield on the floor cable get wired to the neutral lug on the GFCI breaker? Or to ground in the panel?
4-Do I need to ground the metal single gang box the t-stat is mounted to back to the panel ground?
1-Would a 20 amp double pole GFCI be sufficient for the load (considering that I limit the future towel bar heater to less than 10 amps) ?
2-How many conductors do I need from the panel to the t-stat?
3-Does the braided shield on the floor cable get wired to the neutral lug on the GFCI breaker? Or to ground in the panel?
4-Do I need to ground the metal single gang box the t-stat is mounted to back to the panel ground?
#2
Forum Topic Moderator
1-Would a 20 amp double pole GFCI be sufficient for the load (considering that I limit the future towel bar heater to less than 10 amps) ?
2-How many conductors do I need from the panel to the t-stat?
3-Does the braided shield on the floor cable get wired to the neutral lug on the GFCI breaker? Or to ground in the panel?
4-Do I need to ground the metal single gang box the t-stat is mounted to back to the panel ground?
I believe the future towel heater can be connected to your 20A GFI receptacle circuit. Check the instruction manual though for the one you buy.